Hi guys, I'm hoping someone more experienced than me can give me some practical advice because I appear to be going round in circles and I cannot get a straight answer from pH meter suppliers. I'm intending to install a couple of analogue pH probes in a Zone 2 hazardous area with a (safe area rated) powered controller located 10-15m away in a safe area. As far as I can see, the probes are non-powered and only send millivolt signals and therefore these should count as simple apparatus so I should be able to install any analogue probe without issue, but I cannot get a straight answer regarding what barriers need to be used, if any, nor what impact on probe accuracy I'm likely to see if I installed such a barrier between the probe and controller (or indeed if I installed a junction box between the two). It may be that I am going to need a hazardous area rated controller, but I'm reluctant to go to that expense if it's not required. Any advice you can offer would be much appreciated. Sharon
|
|
|
|
Rank: Super forum user
|
DSEAR Schedule 3 and Regulation 7 covers this sort of scenario. You should used suitably ATEX rated equipment unless risk assessment says otherwise......... You should do a specific ignition risk assessment of the equipment. BS60079-0 and BS80079-0 give guidance on how to do these. It sounds though you might have a similar situation to hearing aid and electronic watches which are generally permitted in Zone 2 areas as their energy sources are sufficiently low and they have no sources of self ignition. The data sheet for the pH meter should help with getting the information.
|
 1 user thanked Ian Bell2 for this useful post.
|
|
|
Rank: Super forum user
|
Sorry finger trouble the 2 standards are BS80079-36 and BS60079-0
|
 1 user thanked Ian Bell2 for this useful post.
|
|
|
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.