Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
ttxela  
#1 Posted : 12 July 2023 16:14:06(UTC)
Rank: Forum user
ttxela

Hello Folks

We have a machine that sprays small amounts of Borate Buffer. The SDS lists some fairly serious hazards particularly 'H360 - May damage fertility or the unborn child'  however there is no exposure limit for the UK (although there is for some countries) nor is it listed in EH40. We used to run this machine in a well ventilated area and the operators wore respirators.

The machine is now housed in a room with positionable LEV which can be put over the spray heads. The LEV has been designed to deal with the hazard and has been commissioned etc. with associated reports.

Can we be confident in removing the requirement to wear respirators or should we be doing some exposure monitoring?

peter gotch  
#2 Posted : 12 July 2023 16:53:39(UTC)
Rank: Super forum user
peter gotch

Hi ttxela

Never come across this chemical before!

However, my starting point is that the UK has been decades behind some geographies when it comes to occupataional health risks including, in particular, those which present respiratory risks.

When I joined the HSE there were virtually no exposure standards and we then borrowed many from the American Government Conference of Industrial Hygienists (ACGIH) for the first version of EH40.

My next point is to apply the "Precautionary Principle" - just because something is not listed in EH40 OR the level of risk is not sufficiently documented doesn't mean that you shouldn't take precautions to limit exposure, but so as to apply a proportionate response.

Possibly the documentation you have for your LEV sets out what levels of exposure should be expected now that it has been commissioned and may compare that with international standards.

So, I found an SDS for borate buffer (though the constituents might be different from your substance) which indicates ACGIH Theshold Limit Values of 2mg per m3 as an 8 hour Time Weighted Average and a Short Term Exposure Limit at three times greater 

+ a "(vacated)" by which I assume it means no longer in force OSHA PEL of 10mg per m3 - I assume "vacated" as ACGIH has set a much lower TWA and STEL

+ NIOSH recommending 1mg per m3 so an even stricter recommended limit.

I would like to hope that the LEV is designed to enable exposure to be well under ANY of these limits.

The proof is in the pudding. I suggest you get some sampling done to replicate reasonably worst case operating conditions and see how the numbers play out.

There are so many problems with getting RPE to work as the sellers say it will on the marketing bumph that your objective should be to remove the need for reliance on RPE even as a back up for the LEV (and other technical mitigations), except possibly in relation to emergency scenarios.

So let's suppose the numbers come out as exposure at 0.5 mg per m3 then I think you would have a strong argument not to supplement the technical mitigations with RPE.

Then may be repeat the monitoring at e.g. yearly periods - though possibly if you are getting the LEV performance tested then further environmental sampling might be OTT.

ttxela  
#3 Posted : 13 July 2023 06:34:29(UTC)
Rank: Forum user
ttxela

Thanks Peter, that's very helpful and reinforces my desire for extra monitoring before dispensing with the respirators. ufThe commissioning report for the LEV is silent on levels we should expect unfortunately although I will ask the question.

The SDS we have lists a few other countries OEL which range from 0.5mg/m3 (Germany) through to 10mg/m3 (Lithuania) so I guess a 2mg/m3 aim for us would be reasonable although of course we'd hope to get lower.

Because of the sporadic operation of the machine I'll look for someone who can do some personal monitoring for us I think.

Roundtuit  
#4 Posted : 13 July 2023 09:08:32(UTC)
Rank: Super forum user
Roundtuit

Have you verified the SDS content? The supply chain is incredibly poor at cascading substance information especially formulators who rely upon their substance supplier information.

"Boric Acid" EC 233-139-2 / CAS 10043-35-3 or EC 234-343-4 / CAS 11113-50-1 via ATP 17 (EU 2021/849) is subject to Harmonised Classification as H360fd - this does not necessarily transfer to "Borates".

On the ECHA web site these entries show a Specific Concentration Limit of equal or greater than 5.5% w/w in a mixture in order to apply the classification to the product containing the substance.

This is mirrored on the GB Mandatory Classification List entry.

thanks 2 users thanked Roundtuit for this useful post.
peter gotch on 13/07/2023(UTC), peter gotch on 13/07/2023(UTC)
Roundtuit  
#5 Posted : 13 July 2023 09:08:32(UTC)
Rank: Super forum user
Roundtuit

Have you verified the SDS content? The supply chain is incredibly poor at cascading substance information especially formulators who rely upon their substance supplier information.

"Boric Acid" EC 233-139-2 / CAS 10043-35-3 or EC 234-343-4 / CAS 11113-50-1 via ATP 17 (EU 2021/849) is subject to Harmonised Classification as H360fd - this does not necessarily transfer to "Borates".

On the ECHA web site these entries show a Specific Concentration Limit of equal or greater than 5.5% w/w in a mixture in order to apply the classification to the product containing the substance.

This is mirrored on the GB Mandatory Classification List entry.

thanks 2 users thanked Roundtuit for this useful post.
peter gotch on 13/07/2023(UTC), peter gotch on 13/07/2023(UTC)
ttxela  
#6 Posted : 13 July 2023 11:32:26(UTC)
Rank: Forum user
ttxela

Originally Posted by: Roundtuit Go to Quoted Post

Have you verified the SDS content? The supply chain is incredibly poor at cascading substance information especially formulators who rely upon their substance supplier information.

"Boric Acid" EC 233-139-2 / CAS 10043-35-3 or EC 234-343-4 / CAS 11113-50-1 via ATP 17 (EU 2021/849) is subject to Harmonised Classification as H360fd - this does not necessarily transfer to "Borates".

On the ECHA web site these entries show a Specific Concentration Limit of equal or greater than 5.5% w/w in a mixture in order to apply the classification to the product containing the substance.

This is mirrored on the GB Mandatory Classification List entry.

Argggh, well, no.... Coming from Facilities I'm working on my basic responsibility to ensure the LEV does what it should and takes enough of the hazard away to make sure what is left is not harmful. 

If I understand this correctly we're saying the manufacturer may have made an error in assigning the H360 classification due to the concentration in the finished product due to concentration? 

I'm inclined to believe the SDS and arrange some monitoring, I don't have the resources to doubt every document and work constantly from first principles. Presumably if the SDS has applied the classification wrongly this will then just serve as a reassurance test.

 

peter gotch  
#7 Posted : 13 July 2023 16:58:09(UTC)
Rank: Super forum user
peter gotch

Hi ttexela

I fully take Roundtuir's point, but.....

Given that you have taken the SDS at face value and have already installed and commissioned LEV to mitigate the assumed risk, then it seems to me simply sensible to invest just a little to check that it does mean that exposure to however much of this nasty is controlled to a defendable position.

A Kurdziel  
#8 Posted : 14 July 2023 08:27:44(UTC)
Rank: Super forum user
A Kurdziel

The substance you are talking about is a borate buffer, which is a mixture involving boric acid.  Boric acid has been used for lots of purposes including  in the food sector and in antifungal foot powders.

I am concerned about the LEV you describe as adjustable heads. Does that mean that the operator can adjust the distance between the LEV head and the spray head?  If so how will you make sure that they don’t move it out of the way when it is convenient for them but reduces its effectiveness  to zero. The HSE does not like this sort of  approach. I suspect that they would prefer to ensure the whole process to be  in a booth with operators staying well out of it.  Relying on RPE means that you have to make an assessment about things like how far the spray may travel? Is 3 m from the spray equipment safe or not?  

thanks 1 user thanked A Kurdziel for this useful post.
ttxela on 14/07/2023(UTC)
Holliday42333  
#9 Posted : 14 July 2023 08:48:39(UTC)
Rank:: Super forum user
Holliday42333

I'm aligned with AK on this and would be having another conversation with your LEV designer/installer before formulating additional controls yourself.

If the work is fixed then what is the purpose of positionable LEV?  If it is to allow access to a work piece, can the position be interlocked to the machine or spray?

What is the efficiency of the LEV based on if not bringing the exposure below the exposure levels? How was this calculated?  Don't be fobbed off with a single face velocity calculation as this will be meaningless to exposure control if the head is not in the right place (as previous para).

Has the LEV design and commissioning shown that the exposure is controlled or at the limits of extraction and just minimised ut above the limit; hence still requiring residual RPE?

Your LEV designer/installer shoud have all of this info at their fingertips.  Unfortunatelly I have seen plenty of LEV systems that look pretty but are more hopefull than effective solutions.

thanks 1 user thanked Holliday42333 for this useful post.
A Kurdziel on 14/07/2023(UTC)
Roundtuit  
#10 Posted : 14 July 2023 10:22:04(UTC)
Rank: Super forum user
Roundtuit

Originally Posted by: ttxela Go to Quoted Post
I don't have the resources to doubt every document and work constantly from first principles.

I personally doubt a "lack of resources" would offer suitable defence in a court of law.

Whilst there may be duties upon suppliers to update their SDS in the event of new hazard information (such as an ATP), restriction or authorisation it is frequently the case documents remain in circulation until challenged by those further along the supply chain.

Within my current employment I am frequently presented with documentation that was last up to date two decades ago when the CHiP update arrived at the same time as COSHH was published. Since that time we have had 17 years of REACH, 15 years of CLP, 18 published ATP (not including the changes to candidate SVHC, restriction & authorisation annexes) and the introduction of UK REACH.

Even the "better" suppliers can be out of step with the constant evolution in the legislation so it is prudent to at least check what you are being told.

After all an SDS is merely the basis of information and instructions an employer must transmit to their employee under a COSHH assessment.

Roundtuit  
#11 Posted : 14 July 2023 10:22:04(UTC)
Rank: Super forum user
Roundtuit

Originally Posted by: ttxela Go to Quoted Post
I don't have the resources to doubt every document and work constantly from first principles.

I personally doubt a "lack of resources" would offer suitable defence in a court of law.

Whilst there may be duties upon suppliers to update their SDS in the event of new hazard information (such as an ATP), restriction or authorisation it is frequently the case documents remain in circulation until challenged by those further along the supply chain.

Within my current employment I am frequently presented with documentation that was last up to date two decades ago when the CHiP update arrived at the same time as COSHH was published. Since that time we have had 17 years of REACH, 15 years of CLP, 18 published ATP (not including the changes to candidate SVHC, restriction & authorisation annexes) and the introduction of UK REACH.

Even the "better" suppliers can be out of step with the constant evolution in the legislation so it is prudent to at least check what you are being told.

After all an SDS is merely the basis of information and instructions an employer must transmit to their employee under a COSHH assessment.

ttxela  
#12 Posted : 14 July 2023 12:13:53(UTC)
Rank: Forum user
ttxela

Originally Posted by: Roundtuit Go to Quoted Post

Originally Posted by: ttxela Go to Quoted Post
I don't have the resources to doubt every document and work constantly from first principles.

I personally doubt a "lack of resources" would offer suitable defence in a court of law.

I'm sure that is true, however in deciding how deep to delve into the technicalities of any situation has to be balanced by most folk with the resources available to do so. This is not the only issue/task which is on my plate at the moment and I have to consider the consequences of neglecting others to tackle this or how long I would have to delay dealing with this in order to gather the resources to deal with it in fine detail.

If I understand correctly the suggestion is that the SDS may be overstating the risk so in assuming the SDS correct I hope I am 'playing safe'.

Unfortunately as is often the case in real world scenarios I have inherited this issue from folk who have moved on and left limited information behind so am still in the process of trying to determine why certain decisions were made. I believe positionable LEV was installed as at the time of construction, information on the equipment being installed that generates the spray was unavailable or incomplete. I don't think this was necessarily a bad decision as in fact the heads have to be moved to remove the covers to adjust the machine etc.

Anyhow I'm currently talking to several environmental monitoring companies to determine who can help us measure the potential exposure. I shall update when I have their responses!

A Kurdziel  
#13 Posted : 14 July 2023 13:44:16(UTC)
Rank: Super forum user
A Kurdziel

The problem with an SDS is that it does not provide you with a context for how you are using a substance. That  is down to you and the COSHH risk assessment process. I have just spent 30 minutes explaining to someone  although the SDS suggests that you need RPE if you are handling a particular substance  that really only applies if your are shovelling piles of it with no other controls. They are going to be handling less that a gram in a fume cupboard.  The SDS is correct (probably ) as far as it goes but you need to find out what risk it poses to your staff doing their particular job.  The controls need to be built around that.

Once you have that then you apply the hierarchy of controls with RPE well down the list ( the bottom one being “be careful and don’t breath in the dust”)

Enclosure is always better than RPE and if  you are gong for an enclosure/LEV approach you might as well make sure that it works fully. If you still need RPE then you still have all of the RPE issues: face fit testing; keeping the RPE clean and working properly; making sure people are wearing it; deciding who should be wearing it-just the operators or the people working next to them or across the whole site ( but not in the sales office where it might ruffle people’s hair)

thanks 3 users thanked A Kurdziel for this useful post.
Kate on 14/07/2023(UTC), Roundtuit on 14/07/2023(UTC), peter gotch on 15/07/2023(UTC)
Kate  
#14 Posted : 14 July 2023 14:58:10(UTC)
Rank: Super forum user
Kate

AK - been there, done that, too exasperated to get a T-shirt

Roundtuit  
#15 Posted : 14 July 2023 18:42:58(UTC)
Rank: Super forum user
Roundtuit

Originally Posted by: ttxela Go to Quoted Post
If I understand correctly the suggestion is that the SDS may be overstating the risk so in assuming the SDS correct I hope I am 'playing safe'.

To the extent that AK has mentioned - potentially and unnecessarily spending capital because an (M)SDS has been incorrectly interpreted.

Roundtuit  
#16 Posted : 14 July 2023 18:42:58(UTC)
Rank: Super forum user
Roundtuit

Originally Posted by: ttxela Go to Quoted Post
If I understand correctly the suggestion is that the SDS may be overstating the risk so in assuming the SDS correct I hope I am 'playing safe'.

To the extent that AK has mentioned - potentially and unnecessarily spending capital because an (M)SDS has been incorrectly interpreted.

peter gotch  
#17 Posted : 15 July 2023 16:49:31(UTC)
Rank: Super forum user
peter gotch

Roundtuit - it's a done deal so now time for pragmatism.

Capital has been spent. Might as well spend a fraction of that to see what the LEV (and other technical measures are in place) does in terms of actual exposure.

Review of whatever COSHH assessment (by whatever name) has been done  when time permits might conclude that the LEV is entirely unnecessary and can be decommissioned so as to save on future maintenance and through examination - whilst recognising that it is usually more difficult to make the cogent business case to remove a precaution than to justify it previously. [A couple of years ago I was involved in some asset management that included making decisions as to how often eyewash stations should be checked and how - my comment at the time was that the process giving rise to the risk had been automated, so it was more sensible to remove the eyewash stations].

thanks 1 user thanked peter gotch for this useful post.
A Kurdziel on 17/07/2023(UTC)
Users browsing this topic
Guest
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.