The other angle to look at this from rather than doing volume and air flow measurements would be to check the levels of CO2 in the room.
~/+1000ppm and I would investogate further
Additional resources you can use include:
Building Regulations F:
http://www.planningporta...tf/bcapproveddocuments4/Ventilation Rates 2.10
States the 10l/s per person
HSE Workplace Health and Safety Regulations
http://www.hse.gov.uk/pubns/indg244.pdfWindows or other openings may provide sufficient ventilation but, where necessary, mechanical ventilation systems should be provided and regularly maintained.
Approved Code of Practice: Workplace health, safety and welfare. Workplace (Health, Safety and Welfare) Regulations 1992
http://www.hse.gov.uk/pubns/priced/l24.pdfRegulation 6 - Ventilation
Enclosed workplaces should be sufficiently well ventilated so that stale air, and air which is hot or humid because of the processes or equipment in the workplace, is replaced at a reasonable rate
In many cases, windows or other openings will provide sufficient ventilation in some or all parts of the workplace. Where necessary, mechanical ventilation systems should be provided for parts or all of the workplace, as appropriate.
The fresh air supply rate should not normally fall below 5 to 8 litres per second, per occupant. Factors to be considered include the floor area per person, the processes and equipment involved, and whether the work is strenuous.
HSE General ventilation in the workplace: Guidance for employers HSG202 - May now be outdated as no longer available from the HSE website, however can be found here:
http://www.ucu.org.uk/me...HSG202_-_Ventilation.pdfProvides general guidance on the above HS&Welfare regs
HSE Measurement of air change rates in factories and offices MDHS 73 - This has now been taken out of circulation as well
HSE guidance note EH22 - I cannot find available any more
CIBSE also give recommended guidance on ventilation rates for various workplaces, though you would have to pay for this some details can be found for free here:
http://www.arca53.dsl.pi...om/index_files/vent2.htmI should start charging for some of this info :-)