I’m trying to work out what rating Temperature wise ie T1 to T6, for a piece of equipment in a potential explosive atmosphere. This should be easy, however the substance I’m trying to work this out for is when it is in mist form. I have found some information from an Energy Institute document that states :-
“All petroleum liquids even at temperatures below that at which a flammable vapour will ordinarily form, can be ignited at temperatures well below their flash point when dispersed as a mist…”
Ok, and I know the flash point and auto ignition temp for the substance normally, but how do I find out when it is a mist. Now I know it all depends on droplet size etc, but to be honest I just want worst case. The substance is kerosene, pressurised under its own weight only, which normally has a flash point of between 38 to 72 deg C and auto ignition temperature 220 deg C. The area I feel will be Zone II and Equipment needs to be Category 3 and I feel rated IIA or IIB or IIC would be acceptable, but I became stuck on temperature.
What I’m looking for is worst case for this substance when in Mist or Aerosol form.
Could anyone point me at any guidance or know the answer (I have been looking at the HSE review “rr980” Generation of flammable mists from high flashpoint fluids. Fascinating read all 134 pages of it, but does not provide the answer.
Before anyone asks I’m considering the situation of a pin hole / crack in the container /tank that may produce the mist / aerosol.
Chris
|
|
|
|
Rank: Super forum user
|
When, many years ago, we had a kerosene tank, we assumed that it would just weep.
What is the ambient temperature and what is the ventilation like?
|
|
|
|
Rank: Super forum user
|
Can't you just use ignition energies for a vapour? That has to be worst case right?
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: Super forum user
|
Yes the tank and kerosene are at ambient temp, so more or less what it is outside on any given day. The ventilation varies but generally good (natural not LEV).
Not sure about the vapor Teh Boy. Brain hurts, But the above text indicates that it will ignite at a temp lower than its normal flash point. My understanding is the point at which it can form a vapor mixture with air that is ignitable.
JJ that is of course your prerogative not to contribute to this issue or the forum as a whole. You have at least confirmed there is an easy answer, somewhere.
Descarte8, similar to the ones I read that recommend further research, but no answers. They as did the one I referred to confirm that I seem to be correct to think about this issue.
Sadly it still does not tell me how to calculate, or where to look up the value I need. It is probably in some BSI standard which will cost £100, just to get the single temperature I want.
Thanks all for the input so far, much appreciated.
|
|
|
|
Rank: Super forum user
|
No I disagree JJ, It would be telling if you told me the answer (ie the Temperature).
Have a nice weekend. I intend to do some more research Sunday when My head has cleared from the weeks chaos.
Unless you want to tell me the answer - the temperature is.....
Go on, you know you want to
:o)
Chris
|
|
|
|
Rank: Super forum user
|
Just thought - I know T1 = 450 Deg C and T6 = 85 Deg C etc, but I don't know the lower temperature I should use for Kerosene as a mist, to decide which T number I should specify when buying equipment.
Chris
|
|
|
|
Rank: Super forum user
|
Chris
I think it's BS EN 60079-14:2008 "Electrical installations design, selection and erection" ?
Clause 5.6.2 Gas or vapour which takes you to Table 4
Temp class required by area classification Ignition temp degC Allowable equip
T1 >450 T1-T6
T2 >300 T2-T6
T3 >200 T3-T6
T4 >135 T4-T6
T5 >100 T5-T6
T6 >85 T6
|
|
|
|
Rank: Super forum user
|
Chris
Sorry - hadn't seen your last posting.
|
|
|
|
Rank: Super forum user
|
I work as a design engineer, often designing fuel tanks etc.
Trust me you are over complicating the problem, from how you have described your situation.
Think of the credible failure modes you have ....
|
|
|
|
Rank: Super forum user
|
Not the standard mentioned by Mr Gotch
|
|
|
|
Rank: Super forum user
|
Ok I feel the failure mode will be a pin hole or crack at the base of the tank or ancillary equipment. This would then lead to a jet coming out that could form a mist / aerosol etc.
From the energy institute document I quoted from above the remains of the sentence where I have the dots reads:-
when dispersed as a mist, spray or foam (eg if released under pressure from a leak).
I know the pressure at the bottom of a 6 foot deep tank will not be much, but through a crack or pin hole it could still produce (all be it localised) a mist / spray.
So back to the question which is if it will ignite at a lower temp, what would that temperature be or how may I calculate it. Would the auto ignition temperature remain the same and just the flash point lowers ?
Chris
|
|
|
|
Rank: Super forum user
|
You are on the right lines, but your conclusion is wrong.
Also think of the basic purpose of hazardous area zoning.
Also the purpose of good ventilation
If you read the Energy Institute document to do with hazardous area classification properly it should become clear.
The BS I hinted at gives you the T class for kerosene, this information is also given in the EI document
|
|
|
|
Rank: New forum user
|
Chris
The flash point may well be reduced due to atomised droplets but typically the ignition due to hot surfaces will be several times that of the auto ignition temperature.
Just take the temperature and gas group from EN 60079-20
for Kerosene, this is T3 and IIA.
It is as simple as that
Regards
Laz
|
|
|
|
Rank: New forum user
|
BTW Chris,
You unknowingly had the answer to your question in your first post.
Flashpoint was irrelevent, you could not calculate the flashpoint of the mist/spray due to variable size of droplet.
Consider the flash point of Hexane at -21 degrees C but AIT of 233 degrees, hence T3 and Gas Group IIA based on MESG of 0.93.
Think about it, T6 is a rated surface temperature of 85 degrres and greater. If you based on Flash Point only then no temperature class would be suitable.
You over analysed the problem to hand.
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: New forum user
|
Also consider that the release from a pin hole would result in a zone 2 of negligible extent and it is highly unlikely that you would have equipment or an effective source of ignition operating within the limited extent of explosive atmosphere. The persistence of flammable atmosphere associated with kerosene at normal temperature in anything other that an atomised state is not credible and typically would not be considered as a potentially explosive atmosphere.
|
|
|
|
Rank: New forum user
|
JJ Prendergast wrote:That spoiled it!!
Of course it did :)
|
|
|
|
Rank: Super forum user
|
Thank you both Lazarus and JJ Prendergast.
I did sort of guess as much in a PM today to JJ, but it was a guess. I was happy playing JJ's game he was after all taking me through it and I dare say I would have got there eventually. He also kept the post alive for me.
Yes the use of the tools will be very close to the potential source Lazarus, hence why I have been considering it. I hope a small spray would be noticeable, but the area is crowded with things and so a small mist from the spray may not be spotted.
It's all good stuff anyway.
Again thanks for the help
Chris
|
|
|
|
Rank: Super forum user
|
I must say, that I feel it is better to guide someone to their own conclusions by hinting and suggesting routes of investigation and research is a much better way of helping with problems & queries than giving answers on a plate.
|
|
|
|
Rank: New forum user
|
fair enuf
That me told then.
|
|
|
|
Rank: Super forum user
|
I agree Paul, that way you learn more. I had got there in the last line of my post 15, I just needed a "yes" that was correct.
Again thanks for confirming my thought Lazarus.
Have a nice whatever is left of the weekend all.
Chris
|
|
|
|
Rank: Super forum user
|