I've been asked the question "are we required to unplug and test our Phone system and Network infrastructure as part of PAT testing"
My first thought would be no, a visual inspection would sufficient but then I thought that there could be a need to have it tested and now I'm left unsure! Any help advice on this issue would be very much appreciated
Martin
|
|
|
|
Rank: Super forum user
|
Is the Network 'portable'?
|
|
|
|
Rank: Super forum user
|
Are you planning to test it or fry it. The latter sounds the most likely.
|
|
|
|
Rank: Super forum user
|
OP,
Can I ask where this requirement has originated?
|
|
|
|
Rank: Forum user
|
Stop calling it portable appliance testing.
Does your phone have an electrical connection?
Or is it plugged into a telephone outlet or data outlet?
|
|
|
|
Rank: Super forum user
|
How big is the equipment? Are we talking about a single rack of stuff you can buy off-the-shelf or a whole building of serious stuff?
If it's off-the-shelf and classII, INDG236(rev3) table 1 has suggested intervals for checking equipment. It states that for "Double insulated (Class II) equipment: Not hand-held. Moved occasionally, eg fans, table lamps" visual inspection is required every 2-4 years, and testing is "No".
Unless you're doing something really unusual with it, your phone equipment and network infrastructure is going to be moved around a whole let less fan fans or tables lamps. The equipment in our server room racks is not powered down for PAT testing.
|
|
|
|
IOSH forums home
»
Our public forums
»
OSH discussion forum
»
Portable Appliance Testing - Phone system and Network Infrastructure
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.