decimomal  
#1 Posted : 08 July 2014 11:11:00(UTC)
Rank: Super forum user
decimomal

I am looking confirm my understanding on the requirement for fire doors in corridors. The scenario is a long corridor (circa 30 metres) in a primary school with a fire resistant door at each end. Is there a requirement to provide and additional door in between?
decimomal  
#2 Posted : 08 July 2014 11:22:54(UTC)
Rank: Super forum user
decimomal

I have looked at the HM Guide for fire risk assessment in education and this seems to have the answer.
A Kurdziel  
#3 Posted : 08 July 2014 12:22:07(UTC)
Forum Rank:: Super forum user
A Kurdziel

Having raised this and then found the answer could you share it?
The forum should have rules about this sort of teasing!
decimomal  
#4 Posted : 08 July 2014 12:40:01(UTC)
Rank: Super forum user
decimomal

Apologies, I did not realising I was 'teasing' by not revealing the answer. In summary; where the corridor is more than 30 metres long it should be subdivided near the centre with smoke / fire resisting doors. The complete text is more detailed but readers can find it in the guide ( I don't waqnt to breach copyright).
firesafety101  
#5 Posted : 08 July 2014 14:04:14(UTC)
Rank: Super forum user
firesafety101

They may need to be double swing doors depending on the means of escape.

Don't forget if you create a fire resisting compartment to ensure it is also compartmented above and laterally.
A Kurdziel  
#6 Posted : 08 July 2014 14:20:21(UTC)
Forum Rank:: Super forum user
A Kurdziel

Thanks Decimomal
Sorry but I was curious to find the answer!
Martin Rudd  
#7 Posted : 08 July 2014 15:18:31(UTC)
Rank: Forum user
Martin Rudd

School when built would have been subject to Building Regs approved doc B (Fire Safety ) which from memory is origin of the 30m corridor smoke division doors

Whole range of fire guides at website below. No copyright problem.

This document is also available on the DCLG website: www.firesafetyguides.communities.gov.uk

This publication has been approved by Ministers and has official status. The contents of this publication may be reproduced free of charge in any format or medium for the purposes of private research and study or for internal circulation within an organisation. This is subject to the contents being reproduced accurately and not in a way that implies official status. Any publisher wishing to reproduce the content of this publication must not use or replicate the HMG logo or replicate the official version’s style and appearance, including the design, and must not present their publication as being an official publication as this may confuse the public. The reproduced material must be
acknowledged as Crown Copyright and the title of the publication specified. HM Government does not accept any responsibility for the accuracy and the comprehensiveness of any other versions.
Any other use of the contents of this publication would require a copyright licence.