Please help to settle a debate, should detector heads be Tested for FUNCTION on a weekly basis? I do not suggest that every detector head should be tested weekly, just 1 or 2 so as to ensure each detector head has been proved as operational within a 3 month cycle, (as with call point testing).
Pages 64/65 of "Fire Safety An Employers Guide" (ISBN No. 0113412290
states that
"Electrical fire detection and fire warning systems should be tested weekly for function and to check whether they can be heard throughout the area covered. Make sure they can be seen or heard, particularly by disabled people, and that voice alarms can be understood. They should also be inspected and tested, quarterly and annually, by a competent person.
A colleague disagrees that there is a requirement or need to test some detector heads weekly, and that 6 monthly maintenance inspection and testing by the installer is all that is required.
Your comments are appreciated, thanks.
|
|
|
|
Rank: Guest
|
Posted By Robin B
My understanding is that the call points should be tested on an yearly basis, the sounders weekly and the system and sensors yearly by the installer.
Of course some sytems may not allow call points to be individually tested on a rolling basis but this then should be done by the installers/supply company when they are 'doing' their yearly checks/service.
Robin
|
|
|
|
Rank: Guest
|
Posted By Heather Aston
John
Functional test of representative callpoints and sounders weekly -usually done internally as it's straightforward. (I have not heard of checking smoke detectors on this test before)
System inspected (usually by external company) both quarterly and annually - the annual check is more thorough. Operation of all detectors using a smoke generating thingy at least annually.
Your maintenance company should have the proper intervals for doing each type of test on the quarterly inspections.
Heather
|
|
|
|
Rank: Guest
|
Posted By Chris Black
As an aside, you should probably contact your insurers (who will probably have recentlyappointed themselves as God) as well. Depending on your risk profile they may well have specific requirements for testing in part or all of your premises.
|
|
|
|
Rank: Guest
|
Posted By Merv Newman
John,
read the requirement out loud to the person who is disagreeing : SYSTEMS need to be checked weekly. Setting off a small number of heads in rotation once a week will allow you to test your system. Then get a six monthly maintenance check.
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever
BS5839 is the appropriate British Standard for fire alarms. The recommended weekly tests do not require smoke detectors to be tested.
Call points should be tested weekly in rotation so that if a building has 100 call points it will take 100 weeks to test every call point. In addition to that each zone should be tested once in a period of 13 weeks
Point smoke detectors should be functionally tested once per year (see BS5839: 2002 Part 1 sec 45.4(d))