Hi Chaps
Thanks for your replies, as I suspected there doesnt seem to be anything clear and standard for, how can each company have different sets of rules, strange when I just read on HSE web site that Electricity kills about 25 people a year, as Bob said I have personally seen where 11KV jumped across over 4 feet to a better earth after it traveled up a whole load of pipework, and Garry I do have experience in Power Stations 23 yrs in Malta and 3 yrs in UK.
Don't know if this quote looks familiar to any of you, this is taken from the then Malta Government Electricity Board Generation Safety Rules printed in the 60's or early 70's
Work on Sub-stations and Switching Stations containing exposed live conductors
GE 1 Unless the whole equipment is dead the section which is being made dead for work to be carried out shall be marked or delimited, as far as possible, by use of barriers, notice boards or roping, arranged so that the minimum clearance from the nearest conductor in air to ground level or to platform or access way which may be used when that conductor is live shall be :-
Rated Voltage Clearance
Not exceeding 6.6 kV. 8 ft. 5 ins.
Exceeding 6.6 kV. But not exceeding 11 kV. 8 ft. 6 ins.
Exceeding 11 kV. But not exceeding 22 kV. 8 ft 8 ins.
The word "platform" is used in the ordinarily accepted sense and does not include the tops of transformers, circuit breakers, or other apparatus.
The area to be marked or delimited at ground level shall only be that in which the work is to be carried out.
If the work cannot be carried out without leaving ground level, or such platforms or access ways, the above minimum clearances shall be obtained from the nearest live conductor to the points at which work is being carried out.
If the work is such that these clearances are not sufficient to avoid danger, other suitable arrangements shall be made to provide the requisite degree of safety.
The section shall be distinguished by green flags by day or green lights by night, fixed in prominent positions, supplemented by Danger Notices attached to adjoining High Voltage Apparatus or sections.
Thought maybe something like this exists as the then Malta was under British Rule and all regulations used to reflect those present then in the UK. But I can't find this anywhere.
I also believe there are different distances for Qualified HV personnel like Linesmen Jointers etc. and Non Qualified i.e. like those workers that paint the gates to your Air Insulated 11KV transformer as this CAL/OSHA document suggests.
http://www.ehs.uci.edu/p...ty/hvoltageAppendixD.pdf Thanks all in advance for any information you can provide in light of what I just added.