Posted By Rob Randall I am about to have a debate with a local authority fire brigade about whether an HMO should be compelled to comply with guidance on sleeping accommodation that says that 30-minute fire doors should be fitted to all bedrooms.
The HMO in question is single storey building with a central corridor with two exits, one of which is an emergency exit. The emergency exit has a protected lobby and the travel distances are well within suggested guidance. The HMO complies in all other respects, i.e. regular electrical testing of both portables and fixed system, space heating is a gas fired wet system that is serviced annually by a CORGI registered engineer, all occupants are able bodied, the building has an L2 automatic alarm system with detectors in each room and in the circulation spaces, all of the bedroom doors are close fitting, there are no cooking appliances in any of the bedrooms and the whole building is non-smoking.
In addition to all of the above safeguards the residents are voluntarily undergoing a life recovery programme after a history of substance abuse and have signed up to a strict regime that includes no smoking and no alcohol or other substance use. they are also closely supervised and the Centre is managed by professional carers.
I am of the opinion that the recently published guidance is just that, guidance and that the local authority cannot compel the fitting of fire doors if the risk assessment does not identify them as being necessary.
It begs the question "Can the Fire Authority compel a business to adopt the latest building standards unless they are of the opinion that there is a serious risk to life"
I would be grateful for responses to this question because I believe it involves an important principle.
|
|
|
|
Rank: Guest
|
Posted By Adrian Watson Rob,
The simple answer to your question "Can the Fire Authority compel a business to adopt the latest building standards unless they are of the opinion that there is a serious risk to life" is no, they cannot complel a business to upgrade premises to the latest building standards for two reasons:
1. The building regulations are not retrospective;
2. The RR(FS)O 2005 defines “risk” as meaning the risk to the safety of persons from fire, this means .
|
|
|
|
Rank: Guest
|
Posted By Adrian Watson Rob,
The simple answer to your question "Can the Fire Authority compel a business to adopt the latest building standards unless they are of the opinion that there is a serious risk to life" is no, because the building regulations are not retrospective.
Therefore unless there is a risk to the safety of persons from fire an alterations, enforcement or prohibitions notice cannot be served on the responsible person requiring the upgrading of fire precautions.
However, the onus is on you to prove that the measures that are in place are practical or are reasonably practical, as is necessary!
Regards Adrian
|
|
|
|
Rank: Guest
|
Posted By GT Adrian, I am not sure that ROB has explained whether this is an existing HMO or a change of use. As the answer maybe different.
GT
|
|
|
|
Rank: Guest
|
Posted By pluto Rob,
On the face of it, taking a risk based approach, (single storey, presumably windows from rooms, good though not FR doors, early warning, etc), the premises would seem to be pretty safe. However, Adrian's argument that the building regs are not retrospective is missing the point because the Fire Safety Order most certainly is retrospective, subject to the finding of your risk assessment. (Many older hotels are finding that their 1070's fire warning system cannot meet the new legislative approach). The sleeping guide is just that...a guide and although it should form the benchmark in most situations, it's advice can be modified in certain circumstances.
I wouldn't be too worried about your premises if the existing standards are as you say. One word of caution though, some of the residents may, because of their particular needs, be on some pretty strong (legal) medication. Can you be certain they would all respond to an alarm before the fire broke through the door to the room of origin? Normal 30mins FR doors don't actually guarantee 30 mins.
|
|
|
|
Rank: Guest
|
Posted By Adrian Watson Pluto,
With respect I did not miss the point that the RR(FS)O 2005 could require you to upgrade the fire precautions if there was a risk to the safety of persons.
My comment was "Therefore unless there is a risk to the safety of persons from fire an alterations, enforcement or prohibitions notice cannot be served on the responsible person requiring the upgrading of fire precautions."
Regards Adrian
|
|
|
|
Rank: Guest
|
Posted By Granville Jenkins I can't believe your attitude to such a serious situation... 1/2hour fire doors have been the minimum standard for sleeping accomodation for years - I would suggest that either the architect or perhaps the building contractor skipped over the issue to save costs and put in inferior doors, now it has been picked up by the fire authority and your client is left to pick up the bill.
You cannot rely solely upon the fire alarm system the last line of defence for anyone trapped in one of the rooms is the door.
Regards Granville
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Thanks all for your responses so far.
By way of clarification I should have pointed out that this is in fact an existing HMO and has been so since before 2003. It has had 2 previous inspections by the LAFB pursuant to the licence being granted and they did not, at that time, require the upgrading of bedroom doors to fire doors.
It is also relevant that, at the time the first licence was granted, the premises were already an HMO and there was therefore no change of use and no alterations to the premises have been carried out.
To answer the specific point about things being done on the cheap. My client is more than willing to upgrade the doors to fire doors but he is peeved because he has already recently refurbished the premises and could have had this work done at that time if he had been aware of the Fire Brigade's requirement.
My own view is that the FB have just been undergoing fire risk assessment training and their officer has overreacted.
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Rob it is always difficult to comment on a building that I have not see but it would be very unusual to to have sleeping accomodation of the type you describe without having fr doors. If we play devil's advocate and assume that one of your residents has a fire in his bedroom and he has left his bedroom door open what is in place to protect the other residents and firefighters who will be entering the building?
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi Shaun,
I agree that fire doors are desireable in this situation and that in a perfect world we would have all of the whole gamut of controls in place. The question however is not about whether or not fire doors should be fitted but it is about whether or not the LAFB can insist on specific control measures retrospectively unless they have reason to believe that there is a "serious risk to life"
When you say "it would be very unusual to have sleeping accomodation of the type you describe without having fire doors" that may well be the case where premises have been updated due to change of use etc but not necessarily so in other cases. As I have said the question really is about what element of compulsion can be applied by the enforcing authority and how do they justify it. If they are simply going to apply guidance prescriptively then of what value is a risk assessment and indeed of what value their own previous opinion that the premises were up to a satisfactory standard?
Regarding your "devil's advocate" scenario the protection for the other residents is the likelihood that they will be alerted very quickly in the unlikely event of a fire and will be able to evacuate the premises within minutes. We are talking here about a very small facility of 10 bedrooms with an exit at each end of a central corridor one of which is protected by a 30-minute fire resisting lobby.
I say "unlikely event of a fire" because the likelihood is a part of the equation. In this particular situation the only potential ignition sources are electrical equipment and that is subject to a rigorous regime of testing and examination.
Regards,
Rob
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Rob, what is the statistical basis for you assuming that the only potential ignition sources are the electrical equipment. I don't know the residents as well as you do but I would also be considering the potential for smoking, candles, cooking and arson. In effect you are saying there is zero risk from these other ignition sources. I must admit I would be a little sceptical about this. I would say that the fire service would be doubtful too. You would have to demonstrate to them that what you are saying can be backed up.
Risk assessment is about frequency x consequences. Although you say the frequency of ignition is low, the consequences if a fire does occur must be taken into account. You say that detection will provide the necessary protection. I must tell you Rob you are absolutely wrong on this score. For the detection to operate you must have a fire. Do you know how long it can take for a detector to operate? Do you kow how long it takes for a fire to reach flashover in a small compartment such as a bedroom? Do you know what forces are exerted by a fire reaching flashover in a compartment? Do you know how long it takes some people to rouse from their sleep and be aware that the noise that awoke them is the fire alarm? Do you know how long it will take them to react e.g. deciding that actually the alarm is for real? Do you know what people will do when they open their bedroom door and see a corridor with smoke in it? There are a lot of questions. The consequences of getting this wrong are fatalities, possibly multiple fatalities.
The guidance is just that as you said, but if you do no want to comply with the guidance then you are required to demonstrate equivalency or better in some other way.What you have described does not sound like equivalency to me. I can tell you that the fire service will accept alternative solutions but you have to demonstrate to them that what you are proposing meets the requirements of the RRO.
Now you say that the fire service did not object before so what has changed now. HMO's are where several multiple fatality fires occur, probably more so than any other type of building. Of particular note was the Rose Park nursing home fire. This has influenced a lot of decision making with respect to fire.
You have not persuaded me that there is no risk to life and this is what is the driving compulsion behind the fire service. Demonstrate to them that your standards are equivalent or better than the published guidance and they will not compel you to fit the doors.
One last note. You say that the residents have signed up to non abuse of substances. Even with the best will in the world we all know that some people will find it difficult and may lapse occasionally. It is a difficult road they have embarked upon but I do think this increases the risk.
I'm sorry if this sounds harsh Rob, but I think the fire service are looking at this from a life safety point of view and they rightly can compel you to take action. What they should not do is be prescriptive about what you have to do, but they can give guidance.
|
|
|
|
Rank: Guest
|
Posted By Ken Taylor I was tempted to think that your list of risk controls was reasonable in the circumstances until I noted the nature of the occupancy. From the information supplied, I would expect the risk assessment to follow the guidance regarding fire doors.
|
|
|
|
Rank: Guest
|
Posted By Rob Randall I accept all of what you say about the potential for slower than normal evacuation in the event of fire and the need to take this into consideration.
I perhaps should have said that this is more like a religious community than an HMO. It is a centre run by evangelical protestant ministers for the express purpose of helping former, and I stress the word former, addicts to return to a normal life in the community at large. The residents are all quite clear from the outset that this will involve a rural lifestyle away from temptation with no access to alcohol, tobacco etc. and the management regime is strict.
On the point of ignition sources I must reiterate that there is no possibility of cooking appliances because meals are taken communally and cooking appliances are not permitted in rooms. As already indicated there is no smoking and candles would certainly not be either permissible or even obtainable.
I do accept that FR doors is the norm in this situation and that they are desirable but I still say that the other factors must mitigate the need for prescriptive controls. If they are not to be considered and we are to always assume the worst case scenario then what is the point in a risk assessment?
I will be on holiday for a week and will respond to any replies when I return.
Regards,
Rob
|
|
|
|
Rank: Guest
|
Posted By Ken Taylor I'm sure that the intentions are laudable, Rob. Addicts may, however, remain addicted and devious and, even if completely substance free, have impaired faculty and/or judgement or behavioural problems due to their former lifestyle. Would it be too much to, at least, upgrade the doors to 1/2 hour FR onto 25mm stops (by agreement with the fire officer) - if replacement door-sets are too costly? A comparison could be made with the cost of replacing the building rather than confining a fire to one room until the FRS arrive.
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis Rob
You have probably answered your own question with regards to the recent refurbishment, this almost certainly gave the Fire Service the opportunity to ensure that the doors are now brought up to standard. 1/2 hour doors to escape routes are a standard requirement now days and I personally think the Fire service have been relaxed on the previous visits waiting for a work to be undertaken.
This should have been picked up during the recent refurbishment - was this an external designer? If it was you need to have a discussion with them concerning the omission and their assessment for the lack of change to the doors.
Bob
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Thanks again for your responses but nobody has yet answered the question being put, i.e. what is the point of a risk assessment if prescriptive controls are going to be applied regardless of other factors?
Regarding the refurbishment it was carried out before the previous FB visit and they did not require any changes at that time. They have only commented after the most recent visit for the HMO licence.
Regards,
Rob
|
|
|
|
Rank: Guest
|
Posted By Ken Taylor Life seems to contain a mixture of both prescriptive measures and hazards requiring assessment and control. Prescriptive measures are generally intended to address risk and have been introduced down the ages where unacceptable risks have been inadequately controlled.
Risk assessments need to be suitable and sufficient and it's when the representative of the enforcing authority feels that this is not the case and a hazard is not being adequately controlled that associated intervention is taken - often by reference to published standards or guidance. This can be a little subjective and lead to different conclusions by individuals - particularly within the realms of fire safety. Hopefully the guidance documents under the RR(FS)Order, guidance issued to enforcing authorities and recent revisions to Approved Documents will contribute to less divergence of opinion in future.
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi,
In response to your comments Ken I accept that prescriptive measures and other risk control measures are a fact of life and that is one reason why I make a distinction between compliance assessments and risk assessments when dealing with clients.
My complaint in this case is that the LAFB seem to have only just come to this understanding after having inspected the premises on several occasions over the last 4 years, during which time the sleeping accommodation that they are complaining about has not undergone any structural changes.
It is, I think, a fact that the published Guidance for HMO's is very recent and that the previous standards were much less prescriptive. If the LAFB believe there is a "serious risk to life" then why did they not say so before?
|
|
|
|
Rank: Guest
|
Posted By Ken Taylor I think there is a bit of feeling among the FRS that risk assessment (and the consequences of getting it wrong) used to be more of the duty-holder's lookout but that it's now down to them to make sure it's OK when they visit in case it comes back to bite them if things go badly wrong. Standards of acceptability do change with the course of time and there has been quite a bit of extra training around following the RRO guidance documents. However, I must say that there have always been complaints of inconsistent advice and enforcement between different brigades and inspecting officers - but then H&S people haven't always come to the same conclusions either.
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever 'Thanks again for your responses but nobody has yet answered the question being put, i.e. what is the point of a risk assessment if prescriptive controls are going to be applied regardless of other factors?'
Rob, I believe I did answer your question. You must provide an equivalent solution to the normally prescribed solutions. So called 'prescriptive' requirements are only applied if your current standards are sub-standard and no satisfactory alternative solution is offered. The fact that you have carried out a fire risk assessment and have formed your opinion that everything is ok does not mean that you have satisfied the requirements of the legislation. Obviously the fire service do not agree with your opinion. As mentioned above neither do I. If you want your opinion to be accepted then you must provide better evidence. To do this there is guidance in the form of BS 7974 and accompanying published documents. These are not easy to follow. They are very technical but if you want to deviate from commonly accepted standards then in effect you must offer an equivalent standard. The guidance helps to formulate non-prescriptive standards. Use these as the basis for your discussion with the fire service. I also mentioned that the fire service cannot tell you to follow a 'prescribed' method. All they can do you is advise you that it is one acceptable solution not that you have to follow it.
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi Shaun,
I believe that I have provided satisfactory alternative solutions in the management regime at this location that gives rise to a low or very low likelihood of fire starting. BS 7974 deals with engineered solutions to fire safety mostly to prevent the rapid sread of fire and smoke after a fire has started. As I have already mentioned I believe the likelihood of ignition to be an important part of the equation and one that cannot simply be swept aside by a demand for prescriptive measures.
|
|
|
|
Rank: Guest
|
Posted By GT Rob, You may well feel aggrieved. Kevin Taylor, and Shaun have to my mind explained but, it appears not suffice to satisfy your feelings on this matter.
HMO's are licensed by the local authority who seek comments from the CFO in respect of the proposed use. The cop or guidance docs are compiled from experience and knowledge of how fire develops and affects occupants. Irrespective of the individual officers thoughts on the matter any recommendations are usually vetted by more senior people before dispatching. This is their risk assessment which forms the report, you disagree with it, your prerogative. However, to get a license you need to satisfy the licensing authority.
You can appeal I am sure!
Regards
GT
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi GT,
Firstly may I say that as a professional I am not "aggrieved" by the situation but simply trying to point out the incongruity of the FRS position.
Secondly I do fully understand the process of applying for an HMO licence. You say that the fire brigade have made their risk assessment and have applied the guidance which is based on experience and that is fair enough as far as it goes. What they however have not done is applied the spirit of the guidance which says,
"The provision of fire precautions in an HMO should be based on a risk assessment carried out by or on behalf of the applicant, and reviewed by the relevant officers inspecting the property. The following benchmark standards should not be seen as either a maximum or a minimum, but are intended to provide a reference point for an “average” HMO. They should be applied flexibly, taking into account the physical features of the property and the type of occupants in each case. Officers should always give consideration to alternative approaches, where these can provide an equivalent level of safety."
In actual fact the HMO guidance published by the Scottish Executive does not specify 30-munute FR doors on the escape route unless the property has a storey at a height of more than 4.5 metres and in those circumstances the common stair must be a 30-minute FR compartment.
We may well appeal but I am not interested in scoring points but in clarifying the situation for future reference.
Regards
Rob
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis Shaun et al.
We need to be aware that we cannot risk assess away what are regulatory requirements albeit they are not within the H&S practitioners ambit of work. The Building Regs, part B3 I think, will require fire resisting doors in this type of situation and the fact that these have been overlooked previously does not make it wrong that it has now been picked up. Even the HSE have a general disclaimer that they have not necessarily noted all breaches during a visit.
The reality is that the idea of the FRA was to obviate the need for the Fire Authority/Building control to issue Fire Certificates. The new risk assessments must comply with all the exisiting regulations and codes as the BASIS of the assessment - not replace or otherwise supervene them. The Fire Authority are perfectly entitled, and will, decide that an assessment is not adequate if it does not comply with the codes and legislation already in existence.
If you have standard flush doors opening on to an escape route then these contravene the existing regs etc.
Bob
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Rob, I know BS 7974 gives engineering solutions. Use these:-
- to show the time for activation of your detection system; - to show how long it will take to evacuate the building; - to show how long it will take to reach flashover; - to show your ASET and RSET.
Once you have these you may then produce a compelling argument for your case. Telling them that your management solution is the answer is insufficient.
Robert, we have to be careful about what is 'prescriptive' and what is not. Approved Document B is guidance on how to meet the requirements of the building regs. It is not prescriptive. The objectives of the building regs and the RRO are prescriptive i.e. 'provide a safe means of escape' - how you provide it is not set in stone.
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis Shaun
Whilst not prescriptive one needs to bear in mind the guidance on page 123 of the Sleeping Accommodation guide. The spread of fire and the need for 1/2 hour fire resistance are regarded as vital. I cannot see any Fire Officer going less than this. You have ultimately to recognise that 1/2 hour is the minimum levels that need to be achieved, your risk assessment has to meet this spread of flame criteria at least, it is not a question of escape times. You need to show that any fire will not exit a room in less than 30 minutes otherwise how will you know if the escape route will remain available for the time necessary?
This thinking is exactly the same as the old process required only the Fire Officer then undertook the assessment and set out the requirements. I do not think there was ever an intention that the standards for means of escape etc should be lowered. It is not a question of prescriptive anymore than the requirements say under the WAH regs. Minima have to be achieved by means of a proper assessment within the guidance material set out. The assessment is how you achieve it, ie with different techniques and equipment, not whether you must achieve it.
Bob
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Robert, I do agree with you. I am not advocating lowering standards. What I am saying is that if Rob wants to apply a different set of standards then he must show equivalency. If, for example, he wants to use an oxy-reduct system within the sleeping accomodation then he might use the argument that the oxygen levels are too low for a fire to begin (but sufficient enough to support life). If a fire cannot start then why does he need any doors at all? This might be an argument where the solution is better than the 'prescribed' standard.
I believe if he applies the logic of BS 7974 then I think he will find that he cannot meet the equivalency that is required.
By the way I am not saying that oxy-reduct could be used in this situation - it can't, but what I am saying is that we must not wear blinkers and think there is only one solution to a problem. One possible solution to Rob's problem might be to provide each bedroom with a door to the outside so that no-one has to enter the corridor - no need for fire doors then.
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis Providing of course that they are blocked up to 30 minutes fire protection:-)
At the end of the day the Fire Officers on previous visists and the refurbishment designers should have spotted this problem long ago. It does however highlight the confusion the the FRA is in at times. We seem to regard Risk Assessment as something freer than it actually is.
Bob
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi all,
it seems to me that what you are saying is that the current building standards must be applied in all situations regardless of other factors such as age of the building, cost and other existing controls. Surely this is not the intention of the RRFS Order or the Fire Safety Scotland Act?
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever ?
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi Shaun,
why the quizzical "?" and what exactly is the question?
Regards
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Because Rob your statement seems to be exactly the opposite to what I have been saying. I am saying alternative approaches can be taken and that published guidance does not have to be followed so long as the alternative provides at least an equivalent level of safety.
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis Rob
If you refurbish or upgrade premises the current Building Regs have to be applied. The minute you refurbished the 30 minutes should have followed on logically. Something failed in the system that allowed these doors not to be upgraded. Without more details of the age of the building and the history of work on it one cannot be totally exact on the events. Somewhere somebody missed these doors when the LA issued its licence for the premise.
As Shaun states the assessment must equal or exceed the BR requirements if it is to stand a chance of acceptance. Am I right in thinking this was originally a domestic premise converted for the purpose in which case that is where the problem probably stems from as these do not have the 30 min door requirement. If built for purpose as a "commercial" premise then a designer or contractor has dropped the proverbial clanger.
Sorry to be the bearer of such good news.
Bob
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi Robert,
the current building standards only apply if structural alterations are being made as part of the refurbishment. Minor refurbishment work, such as that done by my client, does not fall within this definition.
The premises have always been sleeping accomodation so there was no change of use.
The HMO licensing regime has been significantly tightened since this location was first granted a licence but the current guidance still does not call for 30-minute FR doors on all bedrooms.
Cheers
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis Rob
In view of your statement that these have always been sleeping accomodation the doors should always have been 30 minutes. The relevant regulations are long established and thus the non compliance started here. They simply failed to meet the BR requirements then in place. You had the baby when the problem was "discovered"
Bob
|
|
|
|
Rank: Guest
|
Posted By Rob Randall Hi Robert,
you say the relevant regulations are "long established". I am not aware of any Regulations that require FR doors on bedroom so I take it you mean the Building Standards?
Regards
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis The door from the bedroom/dwelling area into common areas/corridor has always, from my memory, had a 30 minute requirement. In fact they should, under the regs, have been installed in individual domestic houses of greater than 2 storeys since at least the 1980s. As these are/were commercial from construction there has been no change in the requirement to the best of my knowledge.
Bob
|
|
|
|
Rank: Guest
|
Posted By Crim Fire risk assessment must come into this question, and just because you have the F R A it doesn't mean it is "suitable and sufficient". If you do not use all necessary information i.e. current Regs. and requirements when carrying out the assessment then it may not be suitable and sufficient.
I believe the doors in this case should be 30 minute fire rated as do many others who have contributed, therefore your assessment should have required the upgrade which would resolve the issue without the need for debate with the local authority.
|
|
|
|
Rank: Guest
|
|
|
|
|
Rank: Guest
|
Posted By sauce is'nt an ordinary door about 30 mins fire rated?
|
|
|
|