Posted By Julian Wilkinson I have some concerns over the use of evacuation chairs, not only that the company who installed them are now badgering me to change them as they are 10 years old. The costs are rather significant when you have 16 of them.
My concerns are:
Why change them when they have been sitting on a wall, covered and serviced annually (they still look brand new!)
What is the likley hood of anyone actually using them? (we have a fireman's lift and a refuge area on each floor)we are only eight floors high.
How safe are they to use? Even though we have peopled trained in their use, if the person in the chair is a lot heavier that person holding the chair they risk ending up at the bottom of the stairs in mangled heap! even the trained staff are hesitant about using them.
I don't particularly like them but I have inherited them and would rather have an alternative solution.
I have also heard (but i believe is myth) that these chairs should not be installed above 5 floors?
I suspect this has been a topic of discussion before but i would certainly like to know your thoughts on them.
Thanks
Julian
|
|
|
|
Rank: Guest
|
Posted By FJ We were "advised" that the 5th floor was significant as the ladders on fire engines couldn't reach above this (be good if a colleague in the Fire Service could comment on this) The problem we too have with evac chairs is surely you would need to employ a "Geoff Capes" to carry someone down a long distance. As the you can no longer assume that the Fire Service will take everyone out and so you have to plan how to get EVERYONE out this is much more than a technicality. Although the HSW Act pulls rank over the DDA try persuading a Senior Manager that they are right to face the political fallout of restricting those with mobility problems who cannot safely be removed from say the 25th floor from working there!
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever If you have a firefighting lift and it satifies the requirement of BS5588 part 5 and EN 81-72 then I see no reason why you should not use the lifts as your strategy for evacuating disabled occupants. You must have a rigorous management regime and correct communications i.e. it must be properly planned.
Alternatively I do have a slide showing the use of a parachute for evacuating disabled occupants!
In answer to the query about 5 floors. It is generally true that taller buildings are required to have alternative exit routes as a result of being out of reach of fire service ladders.
|
|
|
|
Rank: Guest
|
Posted By Bob Shillabeer Take great care when using these evac chairs. The organisation I work for has decided not to use them, we occupy the third to seventh floor of a building in London and are very close to the fire station. Luckily we do not currently employ many disabled people but some may occassionally visit us. We have a fireman's lift which is used by the other tennents of the building and each floor has a refuge area with adequate fire protection. It is my view that the problems created by the use of evac chairs outweigh the risk from fire when you take account of the effective use of fire precautions, regular fire drills are conducted and everyone understands thier role in evacuating the building and we also have a mentor sustem for visitors and others who may have mobility difficulties. Evac chairs are risky in thier own way with manual handling and of course additional risk to the person needed to operate them. My view is get rid of them and use a simpler process and get the understanding from the fire authority.
|
|
|
|
Rank: Guest
|
Posted By Julian Wilkinson Thank you all very much for your responses, there is food for thought I must say.
I am about to review our Fire RA and will take matters into account re these evac chairs.
Julian
|
|
|
|
Rank: Guest
|
Posted By Zyggy Turek
I too have grave misgivings about using these hugely overpriced pieces of equipment that usually gather dust & cause more problems than they solve.
Yes, the latest legislation puts the onus on the occupier to safely evacuate a building, but the Brigades are still Fire & Rescue services!
When I discussed this with our FPO's, given that we have refuge areas in our tallest building, & asked the pointed question, would you refuse to effect an evacuation in case of a fire, the answer was an emphatic "no".
Zyggy.
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Zyggy
It is not just the latest legislation that requires you to do this. It has always been the case that it is the employers responsibility for evacuating disabled occupants. It has just become more clear with the latest legislation.
The question is not pointed. It is obvious. Of course the fire brigade will not refuse to rescue people who have not managed to evacuate before their arrival, but the point is that they should not be put into a position of having to do so because there were inadequate management procedures in place. If I were still a serving fire officer I would probably look at that as grounds for prosecution. It would be a failure of Section 15 of the RRO.
|
|
|
|
Rank: Guest
|
Posted By Crim My daughter is 6 years old and physically disabled. She is strong willed and will not sit in an evacuation chair and would have to be man handled into one if it was ever necessary. She would probably then struggle due to being scared which would lead to the carry down becoming dangerous.
With the recent hotel fire in Cornwall in mind you really need to consider your location as to whether or not fire brigade ladders should be included in the escape plan?
|
|
|
|
Rank: Guest
|
Posted By pluto This is a long running discussion with no easy answers. Shaun is right, the responsibility for ensuring the safe escape of ALL persons rests with the employer/owner/etc. Under no circumstances can you factor into your plan "the fire service will rescue disabled people". We start at the reluctance of designers and specifiers, over decades to make premises fully accessible. Then the DDA came along and made it a duty to "make reasonable provision". If you do make this provision, normally, but by no means exclusively, the lift, then you also have to make sure that;
"Where necessary in order to safeguard the safety of relevant persons, the responsible person must ensure that routes to emergency exits from premises and the exits themselves are kept clear at all times. and ...emergency routes and exits must lead as directly as possible to a place of safety; (b) in the event of danger, it must be possible for persons to evacuate the premises as quickly and as safely as possible; (c) the number, distribution and dimensions of emergency routes and exits must be adequate having regard to the use, equipment and dimensions of the premises and the maximum number of persons who may be present there at any one time;
Subsection b is the most relevant here.
I am working on those fire officers who still seem to be giving vague statements along the lines of "of course the beefy firefighter will rescue disabled persons".
Even lifts that do not meet the strict BS/EN standards that Shaun correctly refers to may be considered in certain circumstances.
As for evac chairs...a necessary last ditch evil...probably.
You could try arguing that H & S considerations make the resultant requirements so 'grossly disproportionate' that you can discriminate against disabled persons! You might get away with this for a few more years but not for ever I hope.
|
|
|
|
Rank: Guest
|
Posted By Zyggy Turek Shaun,
Thanks for your comments, I was aware that we have always had a duty to consider the safe evacuation of disabled persons, but as you point out, the RRO is now more explicit.
As a fire safety professional you obviously have your views, but surely to consider a prosecution should be the last resort?
The FPO's I have spoken to are aware of our requirements, but thankfully are sympathetic to the issues they bring.
Together with the DDA & the basic need to consider the feelings of all our occupants in such situations, solutions can sometimes be complex & the use of evacuation chairs is not always the answer.
Zyggy.
|
|
|
|
Rank: Guest
|
Posted By C Kennedy It's also worth considering that not all disabled persons can be transferred into an evac chair due to the severity of their disabilities where transferring them could lead to further injuries to them. The best people to ask about evac chairs are the people who would have to sit in them!
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Zyggy
Prosecution would normally be the last resort but I am referring to if there were a fire, peoples lives were put at risk because of inadequate procedures and firefighters were committed to carry out rescues that they should not have had to do.
Yes in these circumstances prosecution would be an option.
|
|
|
|
Rank: Guest
|
Posted By Melanie Fellows Just a point about evacuation chairs and the strength needed to use them; With the correct training it is possible to carry a person who is much heavier than yourself (when I did my training, the first person I 'evacuated' was at least twice my weight).
The hardest part of the course was actually sitting in the chair whilst someone pushed you down the stairs (really quite frightening at first!)
In my previous employment we had one gentleman who was in a wheelchair on the fourth floor. He never liked taking part in the evacuations and only once went down in the evacuation chair (he didn't want to be the centre piece, which is fair comment).
However, when we had an actual fire, he was more than happy to be assisted out of the building by whatever means.
When considering the pros/ cons of an evacuation chair, remember that the person would need to be able to get themself into the evacuation chair - which does limit who it would benefit.
Melanie
|
|
|
|
Rank: Guest
|
Posted By Sally Interestingly new guidance in scotland makes it very clear that the disabled person need not take part in regular drills and in fact suggest these should be carried out with members of the evacuation team. It also gives lots of information on other methods of evacuating disabled people and is a very helpful and practical document.
It is available at infoscotland.gov.uk/fire
|
|
|
|
Rank: Guest
|
Posted By Mark Eastbourne I believe the issue is down to training regards Evac Chairs.
I was told to use them one way, after trying it this way I put a proposal to the Senior Management Team to look into alternative methods.
However, when they were serviced, I asked the man to show me how to use them.
After I had received this correct training I was then able to easily push a man who weighed a good five stone more than me down the stairs.
Used correctly, I now feel they are an adequate tool evacuaton tool but would recommend constant training and drills!!
Marko
|
|
|
|
Rank: Guest
|
Posted By Graham Bullough When I looked into arrangements for evacuating mobility impaired people from my employer's main multi-storey building some years ago, I sampled what it was like to be a passenger in an evac chair and also the operator of such a device. The scariest part, certainly for the passenger, is when the chair is brought to the top edge of a flight of stairs and tilted forwards so that it can start to descend the flight.
For the reasons already raised by previous responders, my conclusion was that the devices, which my employer already had, should be used as a last resort.
Also, though fire brigades now have "fire and rescue service" in their official titles, the message from fire officers in my area seems to be that their people who attend known or suspected fires are first and foremost "firefighters", and that employers and occupiers have the prime responsibility for arrangements to evacuate people.
Incidentally, for the multi-storey building I mentioned, we have muster points on each floor where mobility impaired people should initially congregate (and each be accompanied by an employee) if the fire alarm sounds. Each point has a phone linked to my employer's control centre. If there is no emergency (e.g. practice being held or alarm is inadvertently set off) the control centre can soon advise anyone at a muster point of this and that there is no need to evacuate.
If there is a real emergency, the control centre knows who is at which locations. This enables arrangements to be made to evacuate them away from the fire location/s and out of the building. This is helped by the fact that the building effectively comprises a number of compartments all separated from each other by horizontal and vertical fire segregation features. However, for some reason, most people do not realise this and wrongly imagine, perhaps from what they've seen in cinema films which are intended to be sensational, that any fire which occurs would immediately engulf the entire building.
|
|
|
|
Rank: Guest
|
Posted By FJ Yes you can indeed take a 5 stone heavier person down one flight- and yes its amazing what can be achieved when you've got a rush of adrenaline in a real emergency- but where do you draw the line- 25 storeys is tireing enough on your own!
|
|
|
|
Rank: Guest
|
Posted By jackw. Hi, Can't believe I am the only one who thinks EVAC chairs are a useful bit of kit. I have used and been in one. My experience.. so long as the people using them are properly trained, undertake in house practice regularly and of course use the correct technique/method when using them, that they are safe and easy to use. The primary problem I have encountered is staff not having the confidence to "push" them out at the start of coming down stairs. This can be overcome by training and practice. Also consider, as we have too, getting disabled staff located above ground floor out of the building during a power cut. Also If my assumption is correct how do the fire service get disabled persons out of a burning building..maybe 10 mins after local staff could have done so using the evac chair. Are we saying fire officers should physically lift the person/put the person over their shoulder? this could cause much more damage to a disabled person (e.g. suffering from brittle bone disorder etc.) than using an EVAC chair. As for staff would can't get them selves into a chair.. those with no ability to weight bare, there are numerous aids that can be used. Also as has been said legislation makes owners/occupiers of properties responsible for getting people out not the fire service, they consider themselves as resuers of last resort. This has certainly been the case in my area and this has been emphasised by the fire service on a number of occasions. i agree that they are a bit pricey, but speaking as a ROLLS ROYCE trained engineer, they are and excellent, technically well designed, manufactured, safe and easy to use
Cheers
|
|
|
|
Rank: Guest
|
Posted By Melanie Fellows Although I didn't state it, I do think evac chairs are a worthwhile piece of kit.
It is definitely all about training (and maintaining the level of competency required to use and control the chair.)
The way that the chair I was trained to used was designed, the chair does the lions share of the work. It's just having the confidence and ability to 'push' someone over the top step, then the tracks of the chair take over.
You only actually tip the chair forward to assist the person to get in or out of the chair - the rest of the time you maintain the angle of the pivot point or slightly tilt it forwards or backwards depending where you are at the time. Keeping within the pivot point means that you take practically none of the weight of the person in the chair (my 18 - 20 stone person took as much effort to control in the chair as a toddler would in a push chair, it's all about technique).
Whilst on the stairs, you could control the chair with one hand (not that I'm suggesting you should though!), you just follow the chair down the stairs, pulling back slightly at the bottom of each flight.
Melanie
|
|
|
|
Rank: Guest
|
Posted By Steve Clark I have recently been looking at the evacuation of disabled persons; my problem with evacuation chairs is the SWL is limited. The particular person i need to cater for exceeds the 150kg SWL of the best Evac chair I can find - any suggestions?
Steve
|
|
|
|
Rank: Guest
|
Posted By pluto Although a bit pricy, (around £7-10K)there are pieces of kit comoing onto the market that allow peple in wheelchairs to remain in their chairs and self rescue down the stairs. The equipment is effectively a mechanical tractor-like stairclimber. It looks a bit odd but, for some large organisations may help solve the issue of very heavy persons. I do not have the link available but those with more knowledge of this equipment may be able to track them down.
|
|
|
|
Rank: Guest
|
Posted By jackw. Pluto there are a number of such devices: stairmatics, climbmatic etc. We have used and still use these for disabled children in some of our mainstream schools. They are very expensive but have the primary advantage of being able to climb stairs thus the person can go up as well as down. However on a cost basis for emergency evacuation it's hard to justify the cost viz an evac chair which does the job adequately. As has been said the key is training in the use of them and continued regular practice = staff confidence in using them, this is paramount. As i said in my first reply I have been in one going down stairs and used one to evacuate staff. I reiterate no problems including the weight/size match of person in the chair viz person taking them down stairs.
Cheers.
|
|
|
|
Rank: Guest
|
Posted By Paul Durkin Regards,Stairclimbers(last three posts) A contact is Manual Handling Solutions: www.manualhandlingsolutions.co.ukThey certainly are good but expensive(£3k)devices & seem easier to operate than the evac + chair,however you may need fewer !! They also have a wt max of 120 to 160Kg. Regards,Paul
|
|
|
|