cantona  
#1 Posted : 17 August 2010 15:26:43(UTC)
Rank: Forum user
cantona

Q) Do PAT test labels have to display the following information: Test date and next test due. My initial thought is no, as long as they have been tested and an electronic record kept this is sufficient. Just need clarification - Thanks
Guru  
#2 Posted : 17 August 2010 15:40:38(UTC)
Rank: Super forum user
Guru

I would suggest best practice would be to label up all appliances that have been tested, with their retest date displayed as a minimum. try the following link for some more info... http://www.pat-testing.info/pat-labels.htm
jwk  
#3 Posted : 17 August 2010 15:42:40(UTC)
Rank: Super forum user
jwk

Hi Cantona, Since there is no requirement to PAT test, and no requirement to label equipment as having been tested, I guess labels can say anything you want. If you are testing (and almost everybody does) and using labels then it makes sense for them to have date of test and a re-test date, but as you say, as long as the information is recorded somewhere and can be easily retrieved that's all that matters. Electrical equipment has to be safe (SFARP), PAT is one way of demonstrating due diligence in this regard, but it's not in itself a requirement, John
MB1  
#4 Posted : 17 August 2010 15:42:42(UTC)
Rank: Super forum user
MB1

I would have thought if you can see at a glance you won't have to ask questions... or anyone else who may take an active interest either?
cantona  
#5 Posted : 17 August 2010 15:49:45(UTC)
Rank: Forum user
cantona

Thanks for that. I take your points on board but as I initially thought its not a legal requirement...therefore I'll go down the pragmatic route and place barcoded stickers/cable wraps on all appliances thus cutting out the cost of purchasing new labels year on year to replace old ones. Interesting to see that its the pat-test label companies that state a test/re-test date should be displayed, or am I just being sceptical? Anyway thanks for your time.
ahoskins  
#6 Posted : 17 August 2010 16:06:09(UTC)
Rank: Super forum user
ahoskins

Although I agree with what has already been said, a label does provide reassurance to the user of the equipment and could flag up a re-test if the 'system' should miss it. They do have their uses.
paul.skyrme  
#7 Posted : 17 August 2010 19:03:43(UTC)
Rank: Super forum user
paul.skyrme

Whilst all of the above info is correct. IF you are PAT testing, and your testers are trained to the C&G syllabus, then they should be abiding by the "bible" the "IET COP". Now in its 3rd revision, IIRC it is referred to in HSE guidance. There in on page 38 Chapter 8.4 Labelling. It requires that appliances are labelled with a unique ID, whether they have passed or failed inspection, the date on which re-testing is due or the last test date and the period to the next test. So in short if you are going to PAT, the only “quasi official” guidance you have is the IET COP which says you must label with this info. So the choice as they say is yours…
Canopener  
#8 Posted : 17 August 2010 19:07:51(UTC)
Rank: Super forum user
Canopener

I can only agree with the majority of what has been said. If a test is required and has been done then it makes absolute sense that a label with the test and retest date is displayed. It's an immediate visual indication to the 'end user' that it has been tested. I would be intersted in arguments against such an approach.
Betta Spenden  
#9 Posted : 17 August 2010 19:17:08(UTC)
Rank: Super forum user
Betta Spenden

PATs are undertaken as a result of an ACoP, Currently 17th Edition. The ACoP (section 8, if I remember correctly), states that the label should display the date of test and the retest date. So thus the “smiley face” labels which say “I’VE PASSED”, do not meet the requirement of the ACoP. Which takes us onto the legal status of PATs and ACoPs.
firesafety101  
#10 Posted : 17 August 2010 19:42:15(UTC)
Rank: Super forum user
firesafety101

Equipment does not have to have the record attached to it, it could be in a ring binder or anywhere sensible. I agree that if readily available it does save time and effort.
paul.skyrme  
#11 Posted : 17 August 2010 21:07:40(UTC)
Rank: Super forum user
paul.skyrme

Betta Spenden wrote:
PATs are undertaken as a result of an ACoP, Currently 17th Edition. The ACoP (section 8, if I remember correctly), states that the label should display the date of test and the retest date. So thus the “smiley face” labels which say “I’VE PASSED”, do not meet the requirement of the ACoP. Which takes us onto the legal status of PATs and ACoPs.
Bretta, You are mixing things up here. There is NO ACoP with regard to PAT. You mention the 17th Edition. This sounds very much like you are referring to the IEE Wiring Regulations 17th Edition, AKA, BS7671:2008 Requirements for Electrical Installations. (On my desk beside me as I type) IF this is the case then you have your facts mixed up. The “17th” stops at the “wall”, the socket outlet the light, the isolator. It does NOT extend to portable appliances, or other devices which are connected to the fixed wiring in the structure of the premises. I have NEVER seen this ACoP section 8 to which you refer, the nearest thing I can find is Chapter 8 which I refer to in my earlier post in the IET CoP, NOT ACoP, ISBN 9 780863 418334. (Also on my desk beside me as I type this.) Where in my quote I refer to the chapter, paragraph & page number of the labelling requirements, this is the 3rd edition of this CoP document. PAT has no legal status, the legal requirement is under PUWER98, EAWR89 etc (you all know the statutory requirements don’t you) for ensuring that equipment is adequately maintained to ensure that it is safe to use. PAT is worthless once the sticker is put on and the equipment is returned to service from a “true” engineering standpoint. Just like the MOT on your car, once it leaves the testing station. ACoP’s are another beast that I am not prepared to enter into debate over. Suffice to say having spoken to Snr. HSE inspectors wrt electrical work etc. I am not prepared to comment or discuss these things on internet forums, even this one, as they are so complex wrt electricity and other engineering matters. HTH, Paul, (Qualified; Electrician PAT tester Designer, inspector & tester of fixed electrical installations, & electrical engineer. BSc. (Hons), MEng, IEng, MIET, oh! & TechIOSH) ;-))
Canopener  
#12 Posted : 17 August 2010 22:28:15(UTC)
Rank: Super forum user
Canopener

I hear what you say Paul however, I am 'confused' (actually I disagree) with your asssertions that PAT has no legal status or that it is worthless. The fact that something has been inspected, and tested and that there is a record for this having been done does carry legal weight, and could be used as evidence in legal proceedings that a duty (may) have been complied with. That to me says 'legal status'. I accept that a lot of PAT is carried out when it is not necessary and carried out more frequently thaan may be necessary, but to suggest that it has no legal status and worthless once returned to service. If we were to use or take your analogy of the MOT, I would again disagree that it is worthless once you drive the car out of the garage (I have heard this argument or non argumaent time and again). The MOT is worth something (rather than being worht nothing or being worthless). I for one take a little comfort in knowing that cars do have to have an MOT periodically rather than not having any. Or do you advocate that they are a total waste of time and suggest that they are scrapped? I know which I am more comfortable with! Sorry - rant over but feel that your no legal status/worthless argument and MOT analogy are fatally flawed
paul.skyrme  
#13 Posted : 17 August 2010 22:54:50(UTC)
Rank: Super forum user
paul.skyrme

Phil sorry the are! However I hear what you are saying. It is basically "due diligence". Which should keep you "out of the smelly stuff"! HOWEVER, I have a friend of the family who runs his own MOT station, so let me give you a true example. He has a taxi in for MOT. He fails it on tyres, insufficient tread. The taxi driver takes it out of the test garage. Gets on the phone and get's another taxi up there from the same co. of the same make. The "new" taxi parks up outside. They swap wheels, he did not realise what was happening as he was undertaking the next test. (It was only after the fact did he get to find out what happened when he tried to find out how things went on so quickly!) The original Taxi is now returned for test with the "good" tyres, he is legally bound to pass it. They pull the 2 taxis on to the road outside and swap the wheels back. The car he has just passed now has illegal tyres. He is powerless to intervene! A similar situation can occur with PAT. Once the item is passed and returned to service it is out of the control of the "tester". So, it could be the case that the "user" when they return the equipment to service drops it on the floor and smashes the case, because they don't normally have to transport the equipment. Thus, the PAT test is invalid before the equipment is returned to “normal” service. Just an example, for the PAT, the MOT is a true situation, however, with regard to the PAT it is a feasible situation. PAT is NOT the BE ALL & END ALL. I would SCRAP PAT as it stands completely if I had my way. Sorry! There are other better ways. The reliance on discrete assessments of condition is unacceptable, take MEWPS & PASMA, they are "similar" engineering situations and are subject to rigorous user checks prior to use to comply with statutory requirements. The only difference is the level of training/instruction etc. required. NOT that simple I know but I hope that it draws a similarity.
Grizzly  
#14 Posted : 17 August 2010 23:24:18(UTC)
Rank: Forum user
Grizzly

paul.skyrme wrote:
Once the item is passed and returned to service it is out of the control of the "tester".
But it is still under the control of the duty holder.
paul.skyrme wrote:
So, it could be the case that the "user" when they return the equipment to service drops it on the floor and smashes the case, because they don't normally have to transport the equipment. Thus, the PAT test is invalid before the equipment is returned to “normal” service.
But if the 'PAT testing', or rather In-Service Inspection & Testing, is being properly adhered to, as per the IEE CoP, then User Checks should also be carried out, and scenarios like the above would be reported and dealt with. Yeah, I know. Pigs might fly.
paul.skyrme  
#15 Posted : 17 August 2010 23:35:35(UTC)
Rank: Super forum user
paul.skyrme

Duck! Flying pig! ;) Most users I come across are not actually competent or otherwise bothered to undertake user checks, expecially once there is a "PAT" sticker on the kit!
Canopener  
#16 Posted : 18 August 2010 08:50:30(UTC)
Rank: Super forum user
Canopener

Paul I don’t want to get into a tit for tat on this. I was challenging 2 things 1. That PAT has no legal status 2. That PAT is worthless I FULLY accept that PAT is not the be all and end all of electrical equipment safety and if you care to read previous threads on similar you will see that I have said the same myself. I would even go as far as to say that both formal visual inspection and user checks play more of a part in equipment safety but that isn’t to say that PAT doesn’t have a part to play, or that it is worthless. Looking at the legal status. If PAT has no legal status I assume using the same logic nor does the formal visual inspection. And taking that further, I assume that no other similar test, inspection or examination (e.g. LOLER) would have lo legal status either (other than the fact that there is a statutory requirement to do them)? Of course, that would be a total nonsense. Any employer who has a regime of portable appliance maintenance in place including testing would be absolutely right in producing that as evidence in court in order to demonstrate that he had complied with a legal duty to maintain his kit. The fact that there isn’t a strict statutory requirement to test doesn’t mean that the test doesn’t have any legal status. Again your use of the taxi MOT example/analogy is ‘interesting‘. Of course you are right and we could all use a similar example, but the fact is that most people take their car for an MOT and where a repair is necessary to reach the standard in the majority of cases this is done one way or the other, without the ’fiddle’ that you are suggesting. I am not sure what similar situation could occur with PAT (changing the fuse to a higher rating?) or what value that would be to the employer or the user to do some equivalent tyre changing scenario with a piece of electrical equipment. Again, returning kit back to service doesn’t make the test invalid. Even though the kit may be dropped and the case smashed; this doesn’t make the test INVALID! Similarly, driving a car away from it MOT test doesn’t make the MOT invalid. Using a piece of lifting equipment after it has had it’s TE doesn’t make the TE invalid. I have to say that is a very strange (obtuse) way of looking at things.
paul.skyrme  
#17 Posted : 18 August 2010 16:41:34(UTC)
Rank: Super forum user
paul.skyrme

Phil, Sorry I don't want a tit for tat either, it was late last night when I posted perhaps it would have been better not to! Your points, , Ok it does go to proving "due dilligence" in a manner of speaking. My point was not made well. An annual formal inspection & test is OK on some kit, unnecessary on other kit, and woefully inadequate on other kit. As part of a regime of in service inspection & testing of electrical equipment including user inspections, checks and formal inspecitons & tests then that is acceptable. My gripe is the way it is run by a lot of organisations. 2, it is not worthless, IF it consists of more than an annual formal inspection & test of all equipment. This is the bit that gets me, where everything is formally inspected and tested annually regardless. LOLER & other inspections are covered by ACoP's PAT is not, it is ONE way of complying, NOT the only way. This is another of my gripes with it. Everything must have a valid PAT test label, which is NOT correct. OK I did not word my post overly well! However, once the examination, any examination is over, & the equipment is returned to service etc. then it is in control of the user, so the results of the examination of whatever type could be "changed" in seconds by damage, overloading etc. My point is to try and make people think that just coz it has a PAT sticker it is safe, and if it does not it is not safe. Also, with LOLER, MEWPS, PASMA stuff then it is inspected prior to use is it not? My point with PAT is that users don't do this, they don't understand what to check, how to check and have the opinion that if it has a sticker it is safe to use. I just feel that the blanket view is not vaild and is in danger of bringing in a complacent attitude. IF there is a good regime of encompassing the whole of the PAT system then it can be good. However, you cannot correctly undertake a full formal visual inspection & test on an item of electrical equipment and correctly and adequately document this @ 50p per item, nor £1, nor £1.50. The system is failing as it is cost driven, not safety driven. Also, the buck shifting is an issue I have, Regina Vs Octel is somethign I often explain to potential PAT customers who want to pay less than £1 per item. The laast issue IMHO is the interpretation of PAT. Which is why I feel that it is inappropriate. It is NOT the once a year (etc.) formal visual inspection & test, it is a safety management system of electrical appliances and other equipment.
jwk  
#18 Posted : 18 August 2010 16:57:24(UTC)
Rank: Super forum user
jwk

I agree with Paul on this one, LOLER checks are required by legislation, PAT is not. My original statement is not that PAT has no legal status, it was that it is not a legal requirement. Of course it has a 'legal status' in that it would be evidence in court of due diligence in maintaining electrical equipment safe SFARP. It is not, however, a legal requirement; there is no statute which requires it, and safe SFARP can be demonstrated in other ways, John
Clairel  
#19 Posted : 18 August 2010 17:22:06(UTC)
Rank: Super forum user
Clairel

I think that once again forum users are getting in a pickle about different uses of terms. In this case I think people are using the term 'legal status' to mean different things. PAT is not a legal requirement but it can be used as evidence in legal proceedings. Yep we all know that PAT is not a legal requirement but do we all use the term PAT to mean different things? Lets get this clear that PAT in it's own right will not clear you in court if something has gone wrong becuase it is just one of a range of measures that needs to be employed. As others have said PAT just shows safety at that moment in time and so unless regular visual checks are made as well you would not have done enough. Nothin annoys me more than an item of equioment with an 'in-date' PAT label and bare wires showing or damaged cabling. If we use the MOT analogy that is being used and combine it with the tyres example then you can apply it to safety of electrical equipment. MOT a car and it says that is safe at that point in time but you can still get nicked 5 mins down the road for having bald tyres. The MOT is not a get of jail free card. Equally your item of electrical equipment can have a PAT lable on it but if the cable is damaged an inspector can put a prohibition on the item (or when I was doing it ask them to cut the plug off!!). Again PAT is not a get out jail free card. PAT (And MOT) are only one of a range of measures that need to be taken to comply with the overall requirement. It's where many companies are falling massively short of doing what is necessary. By the way there is no legal requirement to display test dates, it may be best practice though.
jwk  
#20 Posted : 18 August 2010 17:33:47(UTC)
Rank: Super forum user
jwk

Claire, I agree entirely, John
paul.skyrme  
#21 Posted : 18 August 2010 17:51:35(UTC)
Rank: Super forum user
paul.skyrme

Thank you Clairel, as I understand it that is very similar to the stance taken by some of your ex-colleagues I have talked to who are fellow members of the IET in my area. I won't mention the organisation, if I understand your background then suffice to say we have all heard of it? My comment on dates comes from the IET CoP. My idea being if you are going to do it you should do it as per the nearest thing you have to an ACoP, which as I see things is the IET CoP. This is referred to in several HSE documents as I understand things?
paul.skyrme  
#22 Posted : 18 August 2010 17:53:30(UTC)
Rank: Super forum user
paul.skyrme

Clairel, One thing about cutting the plug off, I agree very effetive, but, then you can put the plug in a socket and get a shock off the cut ends! ;) I do this myself, but, I also damage the plug so it cannot be inserted into an outlet! Sorry, just being wicked! Again........
Betta Spenden  
#23 Posted : 18 August 2010 21:16:26(UTC)
Rank: Super forum user
Betta Spenden

paul.skyrme wrote:
Betta Spenden wrote:
PATs are undertaken as a result of an ACoP, Currently 17th Edition. The ACoP (section 8, if I remember correctly), states that the label should display the date of test and the retest date. So thus the “smiley face” labels which say “I’VE PASSED”, do not meet the requirement of the ACoP. Which takes us onto the legal status of PATs and ACoPs.
Bretta, You are mixing things up here. There is NO ACoP with regard to PAT. You mention the 17th Edition. This sounds very much like you are referring to the IEE Wiring Regulations 17th Edition, AKA, BS7671:2008 Requirements for Electrical Installations. (On my desk beside me as I type) IF this is the case then you have your facts mixed up. The “17th” stops at the “wall”, the socket outlet the light, the isolator. It does NOT extend to portable appliances, or other devices which are connected to the fixed wiring in the structure of the premises. I have NEVER seen this ACoP section 8 to which you refer, the nearest thing I can find is Chapter 8 which I refer to in my earlier post in the IET CoP, NOT ACoP, ISBN 9 780863 418334. (Also on my desk beside me as I type this.) Where in my quote I refer to the chapter, paragraph & page number of the labelling requirements, this is the 3rd edition of this CoP document. PAT has no legal status, the legal requirement is under PUWER98, EAWR89 etc (you all know the statutory requirements don’t you) for ensuring that equipment is adequately maintained to ensure that it is safe to use. PAT is worthless once the sticker is put on and the equipment is returned to service from a “true” engineering standpoint. Just like the MOT on your car, once it leaves the testing station. ACoP’s are another beast that I am not prepared to enter into debate over. Suffice to say having spoken to Snr. HSE inspectors wrt electrical work etc. I am not prepared to comment or discuss these things on internet forums, even this one, as they are so complex wrt electricity and other engineering matters. HTH, Paul, (Qualified; Electrician PAT tester Designer, inspector & tester of fixed electrical installations, & electrical engineer. BSc. (Hons), MEng, IEng, MIET, oh! & TechIOSH) ;-)) Best you go back and read it again then Mr Post Noms.
paul.skyrme  
#24 Posted : 18 August 2010 21:35:26(UTC)
Rank: Super forum user
paul.skyrme

Sorry Bretta don't need to. You have not made it clear the document you are referring to. IF this is BS7671:2008 it DOES NOT APPLY to portable appliances end of. I cannot decipher your post any other way sorry. I work with this almost every day & I am unable to see how this document can apply to portable appliances etc that are within the scope of the IET CoP I also refer to. I checked them last night before I posted. IF you feel I am wrong please quote from the relevant documents, as I have them to hand to cross reference to. Otherwise I cannot follow your reasoning. Please elaborate futher your argument becuase I cannot understand your point from your posts. The IET CoP is NOT an ACoP, end of. IF you read my previous posts, those of Phil Rose & Clairel I'm sure you will begin to understand the scope of PAT & how it is abused. IF you feel I am wrong please explain and quote from the relevant documents where you feel my error lies and then if you are correct i will retract my statements. Page & chapter references will be fine as then it will nto breach copyright and I have them all to hand. Paul.
paul.skyrme  
#25 Posted : 18 August 2010 21:36:23(UTC)
Rank: Super forum user
paul.skyrme

sorry about the typo
toe  
#26 Posted : 18 August 2010 22:51:29(UTC)
Rank: Super forum user
toe

Forums are Great, Just like our health and safety meetings never stick to the adgenda (origional post) and we argue about litle trivial points. My point is; as a previous MOT tester, I would like to think that all of the vehicle that I failed the MOT test because of serious safety related issues for example bald tyres or dodgy brakes, and these were fixed before a re-test and new certificate issued, that because I tested and failed the vehicle that I may have saved a life or prevented a serious injury from happening. I am also sure that if a failed piece of electrical equipment and was taken out of service then in the intrest of safety in any book this has got to be a good thing wether legaly required or not. Also have to agree to the statement that a lot of PAT is cost driven and not safety driven, my experience being that I had come accross a piece of equipment that was tested and passed with soldered wires and electrical tape wround the cable, later found the company only paid 50 pence per item.
paul.skyrme  
#27 Posted : 18 August 2010 23:02:04(UTC)
Rank: Super forum user
paul.skyrme

Toe, This is at least part of my point! The dodgy tyres bit can be fixed and then unfixed though as per my post! Also your point about cost vs safety driven is again part of my argument. I have come across large fixed electrical equipment with wiring on the verge of catching fire, it had melted to the extent that it caused a no start fault, at which point I was called. However it had recently been PAT tested! The kit weighed over 12 metric tonnes. It was 3ph on a Y/D starter with a DC inejection brake. It was fixed to the stcutcture of the building and the control system was part on the machine & part on the building structure. The control system does not comply with PUWER98, however regardless it has been given a PAT pass within the last few weeks. The wiring defect had been previously reported, and dismissed because the PAT co. had not picked it up and the company that highlighted it did not have it as part of their service provision remit. Even though they were more competent to assess and report on this equipment. Obviously given the state of the wiring etc found! This is another "problem" with PAT it being taken out and applied to equipment that it was never intended to cover, along with utilising personnel that are not capable of inspecting complex and unusual systems of which they have no experience and that would not have been covered on any standard PAT course, the C&G one included. How?
pete48  
#28 Posted : 19 August 2010 11:43:31(UTC)
Rank: Super forum user
pete48

A short input with some personal experience. At least 90% of all SME that I visit will respond to a question about their electrical safety with "we PAT 'test'-go check the labels". When I then say "and......?" I am mostly greeted with a nonplussed stare. In some cases I am told that I cannot know what I am talking about because the PAT man checks EVERYTHING each year! That is the real issue with PAT. It is a minor part of a programme misunderstood by many perhaps as result of the marketing success of those who carry out PAT on a priced contract or maybe not. The problem often is that many SME contract out stuff without looking into what they are buying, not that companies are out there selling their services. Rather like the conkers bonkers stuff; their perception of PAT is not reality but it is nonetheless real. We do need something to change that perception. p48 ps Paul actually answered the OP question at post #7 but I enjoyed reading the input since. What would we do without RIDDOR and PAT on this forum?
paul.skyrme  
#29 Posted : 19 August 2010 22:15:09(UTC)
Rank: Super forum user
paul.skyrme

pete48 wrote:
A short input with some personal experience. At least 90% of all SME that I visit will respond to a question about their electrical safety with "we PAT 'test'-go check the labels". When I then say "and......?" I am mostly greeted with a nonplussed stare. In some cases I am told that I cannot know what I am talking about because the PAT man checks EVERYTHING each year! That is the real issue with PAT. It is a minor part of a programme misunderstood by many perhaps as result of the marketing success of those who carry out PAT on a priced contract or maybe not. The problem often is that many SME contract out stuff without looking into what they are buying, not that companies are out there selling their services. Rather like the conkers bonkers stuff; their perception of PAT is not reality but it is nonetheless real. We do need something to change that perception. p48 ps Paul actually answered the OP question at post #7 but I enjoyed reading the input since. What would we do without RIDDOR and PAT on this forum?
Pete48, Thanks for that comment I know I did, however, my reasons for continuing the thread were to basically challenge the thoughts etc. to ensure that the general perception of PAT is brought into the real world. I notice that there have been no statements of fact from the relevant IET documents to dismiss or refute my comments! BTW mine are still along side me should anyone wish to point out where my interpretation is wrong and then I will look up their references and provide appologies etc. based on those references if necessary. Paul
118ncg  
#30 Posted : 20 August 2010 07:47:50(UTC)
Rank: Forum user
118ncg

Portable Appliance Testing (PAT) not PAT testing not good english... See HSE myth of the month believe April 2007 Depends on what type of equipment you want to check Class 1 or Class 2 Indg 236 gives basic advice for portable stuff see hsg 107
Grizzly  
#31 Posted : 20 August 2010 09:28:15(UTC)
Rank: Forum user
Grizzly

paul.skyrme wrote:
I notice that there have been no statements of fact from the relevant IET documents to dismiss or refute my comments! BTW mine are still along side me should anyone wish to point out where my interpretation is wrong and then I will look up their references and provide appologies etc. based on those references if necessary.
I shouldn't worry about it too much, Paul. I reckon Betta realised he/she had got hopelessly confused, and was talking complete rubbish, and so just decided to be a bit facetious with their second post.
firesafety101  
#32 Posted : 20 August 2010 09:42:17(UTC)
Rank: Super forum user
firesafety101

The car MOT is useful as without it you cannot road tax your vehicle if it is over three years old.