Phil,
Thank you for the vote of confidence!
However, it is Skyrme, NOT Skymes! ;)
Chris it is "volts that jolts" but "amps that kills".
I have had many electric shocks over the years in the 10's of thousands of volts.
If anyone "played with a Van De Graff generator at school, college or uni that could generate such voltages, however the current is minuscule.
"static" shocks from the ignition systems of cars etc are also often thousands of volts but nano, micro or milli amps. Beware of the old magneto ignitions though they had some current behind the spark!
My explanations may not be rigorously technically correct, however, I hope that I have "modified" them to explain the situation in a better manner.
Ok as far as construction site supplies, Phil is correct the "normal" 110V a.c. on a "site" as supplied from a "yellow" transformer type supply is what is know in the trade as CTE, that is centre tapped earth.
In this scenario you only achieve circa 55V to true earth potential, RMS that is.
Below 50V a.c. is considered "harmless", think of it, if you put your hands across your car battery which is capable of delivering several hundred amps in seconds to drive the starter motor, however only at 12V d.c. you probably felt nothing, I know I did every time I did it!
The joys of youth eh!
OK, Ray is also correct that in the wrong situation a current at 50V a.c. can kill, certainly 0.5A can kill, a.c. or d.c. depending on how it is applied to the body.
The reason we look at 30mA as additional protection against electric shock in general electrical installations is that "most" humans can withstand this level of current for half a 50Hz a.c. cycle IIRC. Thus it is a survivable shock, trust me it is! Please don't ask any more!
If you are serious about getting "into" this you need to refer to IEC TR 60479 which is an IEC (International ElectroTechnical Committee) report on the physiological affects of electric shocks of varying currents and voltages on humans and animals.
BTW 4 legged beasts are more susceptible as they have 4 points of contact and can have a larger voltage differential between their points of contact.
Impedance is not the collective name for resistance and electric shock it is the collective name for the "resistance" to an a.c. electric current caused by resistive, capacitive, and inductive affects to the flow of said current.
Chris, you DO have my mobile no. if you need it, already, else PM & I'll give it to you again as this may be a little difficult to explain on here, though I am willing to try, thus keep this discussion in the general body of info!
Not sure at this stage what else to post?
The risk of a shock from correctly maintained power tools even on a construction site is quite small really IMHO.
Remember 240V a.c. supplies on construction sites should be protected by a 30mA RCD. These will then be supplying the 100V a.c. CTE step down transformers.
Thus the energy at the 110V side will be limited to the 30mA incoming earth leakage current at 55V to earth, "not rigorous I know" also as the equipment is already in good condition the operator should not come into contact with the electrical supply should they?