Hi Tom
There are three key "deliverables" with CDM:
1. The "pre-construction information"
2. The "construction phase plan"
3. At least one "health and safety file" to inform work in the future on handed over assets.
Nowhere does CDM mention a "design risk assessment" and may be you don't need a document with that title.
Now I don't know what 2 day course this PD has been on, but attending a 2 day course does not a PD make.
Under CDM 2007, the PD (along with every other duty holder) had to be "competent" but that word was replaced with a requirement for "skills, knowledge and experience" in CDM 2015.
Problem is that the guidance supporting CDM 2015 was made deliberately "lite" to keep a deregulatory minded Government happy and one of the results is that it provides much less clarity than the Approved Code of Practice and guidance that supported CDM 2007 - which you can probably still find on the HSENI website if you search for L144.
So, one of the basic principles of CDM 2007 was that each duty holder including the forerunner of the PD was entitled to assume that the Client would NOT appoint designers and contractors who were NOT competent.
Thence it was unnecessary to tell a contractor "how to suck eggs".
You didn't have to say that a scaffold needs to have proper foundations, good foundations, ties and bracing, guard-rails and toe-boards etc.
Instead you needed to tell that contractor about the "significant risks", which was defined on page 98 right at the end of L144:
(a) those risks which were not obvious
(b) those which were unusual
(c) those likely to be difficult to manage
If you follow that principle then you can work out what should be in the pre construction information (and also the health and safety file or files) and what is best omitted not least as it is likely to obscure the information that is important.
So, may be all that information about "significant risks" could be on drawings e.g. in so called SHE boxes.
But, it is very unlikely that all the significant risks have been designed out.
The chances are that this modular construction is NOT in the middle of nowhere. So, there will be site specific issues that need to be brought to the attention of duty holders.
Whether that be a school adjacent to the delivery route, overhead and underground services, ground contamination etc etc.
Presumably the modules will be craned in, so are there constraints as to the positioning of the crane. Do you need to construct foundations simply to give the crane a safe place to operate from?
...and you might have rules set by the Client as to their minimum standards, which may or may not be hidden deep in the Contract specification. Better in a standalone document (AS WELL) to highlight them.
Personally my starting point would be the list of issues to be addressed in L144, so that if only for assurance you can say "yes, that is covered on drawing X and doesn't need further comment", "that is not applicable to this project", "that is in the site investigation report" etc etc.