Hi Jdpnsp
First let me mention that I don’t know what material your biomass pellets are made up from and if you have had a DSEAR Assessment completed to identify if there is an actual explosion or increased fire risk identified during the delivery process or at any other time that during the consumption of the biomass pellets.
It really depends on particulate size and amount of dust being generated. The pellets themselves are not an issue, it is the fine dust that forms part of the delivery and is also generated when they are delivered the pellets to the silo form the delivery vehicle under pressure. You don’t mention what the pellets are made from so on this occasion I am assuming they are compressed wood powder, sawdust and chippings.
The dust generated from the aforementioned substrates is the same particulate size if not smaller than wood flour. Normally the vehicle delivering the pellets connects an extraction fan to the silo to extract the dust during the delivery process through a filter to a safe location outside the building.
This has a two-fold function. First it reduces the pressure within the silo during delivery as the pellets are delivered. This prevents the dust that is generated being expelled into the room were the silo is located through gaps in the structure as it is not a certified pressure vessel.
Secondly the dust is potentially explosive and preventing it leaving the silo into an enclosed room with potential ignition sources (as these biomass silos are normally located in the same room as the boilers) which can also be sometimes gas fed as an alternative fuel source.
Generally hard wood flour has a Minimum Ignition Energy of 20mJ but needs 50g/m³ to become ignitable, whereas Pine wood flour has a Minimum Ignition Energy of 40mJ but surprisingly only needs 35g/m³ to become ignitable.
Passing particulate either pellets or dust along a duct from the delivery vehicle into the silo has a charging affect and to reduce this charging action it is important to ensure that the silo and delivery vehicle are at the same potential if the ducting is not static dissipative. To aid this a grounding wire is attached form the delivery vehicle to a common earth point where the silo is also grounded.
The guidance you require on this subject matter is held within PD CLC/TR 60079-32-1 Explosive Atmospheres Electrostatic Hazards, Guidance.
Section 7.2.4 Promoting charge dissipation
“In situations where it is not possible to avoid a flammable atmosphere, the risk of ignition can be controlled by limiting charge accumulation. For the components of the handling system, this involves bonding solid conductors and people to ground and, if necessary, replacing insulating system components with earthed dissipative or conductive components “.
This applies to both dusts and liquid delivery where there is a risk of an explosive atmosphere being generated within a silo or tank which is why they are grounded during delivery.