I currently work in a Food Factory and have been asked what the frequency is for the testing of the electrical installations on site.
Can anyone give me some advice on this matter.
K. Wood
|
|
|
|
Rank: Guest
|
Posted By Jack
You need BS 7671 Requirements for electrical installations.
I think the frequency in 5 yearly, but check the standard.
|
|
|
|
Rank: Guest
|
Posted By Paul Bellis
BS 7671 (732-01-01) - states that Initial verification needs to be carried out on electrical installations being first put into service and inpections carried out thereafter and tests to verify. Any alterations or additions to an installation should similarily be verified to comply with regulations. With regard to periodic testing - BS only says the frequency of inspecting and testing of an installation shall be determined by the type of installation its use and operation, the frequency of maintenance and the external influences to which it is subjected. It sounds a bit like the HSE guidance to risk assess everything without giving any concrete periods etc.. however the IEE 16th Edition regs give a general rule of thumb guidance of ...periods not exceeding
Domestic installations - 10 years
Commercial installations - 5 years
Industrial installations - 3 years
Leisure complexes - 1year
Temporary sites ie construction sites etc - 3 months
however again shorter intervals are recommended dependant on the nature of activities and installation.
hope this helps