Are there any experts out there on Kerosene storage?
Forum Rank:: Guest
|
Posted By Rachael Powell
I have been asked by a friend who has a 2500 storage of kerosene on their work premises for heating supply. It has a suitable container but no bunding was constructed with it. I have said that it should be bunded but the company will not listen to reason. Does this fall under the 'The Control of Poluution Regs & DSEAR regs also?
It is also close to a fresh water drain & guttering is about 1 metre away? There is no room around the container either....should it be removed?
|
|
|
|
Forum Rank:: Guest
|
Posted By Jonathan Sandler CMIOSH
is the tank itself bunded or double lined?
|
|
|
|
Forum Rank:: Guest
|
|
|
|
|
Forum Rank:: Guest
|
|
|
|
|
Forum Rank:: Guest
|
Posted By Rachael Powell
The Talking Titan ES2500B - it says under the description on the manufacturers website 2500 and above should be fitted with a bund???
|
|
|
|
Forum Rank:: Guest
|
Posted By Fred Pratley
The following is extracted from the Environment Agency leaflet on the Oil storage regulations
Which types of oil are covered?
All types of oil, with the exception of waste oil, are
covered by these regulations, including petrol, diesel,
vegetable, synthetic and mineral oil. Waste oil storage
is covered by the Waste Management Licensing
Regulations.
Kerosene is simply another form of oil, so you are correct, it requires bunding etc.
regards Fred
|
|
|
|
Forum Rank:: Guest
|
Posted By Neil Koskie
The Oil Storage Regs apply to 200 litres or more and Kerosene is covered under the Regs as previously stated.
The key requirements are:
1. There must be a bund to intercept any leaks from the container and its pipework.
2. The bund surrounding the tank should have sufficient capacity to contain 110% of the maximum content of the tank.
3. Above ground pipework should be supported and underground pipes should be protected from incidental damage and have leakage detection.
4. Rainwater drainage should not be allowed to enter the bund.
5. The bund walls and base should be periodically inspected and must be constructed from impermeable materials.
Hope this helps
Neil
|
|
|
|
Forum Rank:: Guest
|
Posted By Salus
Rachael, as Neil, also if there is a significant risk, e.g. oil stored within 10 mts of inland freshwaters or coastal waters or within 50 mts of a well or borehole, you will need to bund the storage.If you cannot do this with your existing storage you will have to relocate.just make sure that your company took all reasonable measures to prevent any foreseeable pollution scenarios
|
|
|
|
IOSH forums home
»
Our public forums
»
OSH discussion forum
»
Are there any experts out there on Kerosene storage?
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.