Posted By Alan E McKerns Would i be right in saying that emergency escape lighting in an office area should be fully checked at least annually?
In the middle of a FRA.
Cheers Alan
|
|
|
|
Rank: Guest
|
Posted By Esther Bucklee Emergency lighting should be checked monthly, 3 monthly for 1 hour and at 6 months it should have a 3 hour test.
|
|
|
|
Rank: Guest
|
Posted By Gff and the unswitched mains indicator daily, but this does not need to be recorded.
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Monthly – flick test Annually – full duration test
BS 5266 part 8: 2004
There is no longer a requirement for 6 monthly tests and the full duration test depends on the batteries used. Some are 3 hours some are only 1 hour.
|
|
|
|