Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
mattyturton  
#1 Posted : 27 May 2011 11:29:14(UTC)
Rank: Forum user
mattyturton

Hi All

Can anyone please point me in the direction of the regs I need to read regarding gas safety in a schools environment?

Or advise the current thinking regarding Gas safety shut off valves in classrooms-ie whether they are ok to be manual shut offs or should they have all been replaced with automatic/electrical shut offs?

Thank you in advance for your help.

Best regards

Matt
bob youel  
#2 Posted : 27 May 2011 11:56:02(UTC)
Rank: Super forum user
bob youel

Matt; what is your employment role so as I can help; as if you are not a H&S person I advise that you get one to advise you

The reason I ask the question and present the advice that I have is because many schools are now dropping H&S professionals in favour of well meaning people whereas professionals / people training to be professionals should be employed
phow  
#3 Posted : 27 May 2011 12:00:16(UTC)
Rank: Forum user
phow

Matt. The old Corgi site [registration is now via Gas Safe] has information on non-domestic gas systems.
http://www.corgi-direct.com/non-domestic/_/ghbnd. My personal assessment is a manual valve, well signed, and out of accidental knock off range, would be best. You can see when it is on and when it is off. + Cheap and simple. Automatic always have to be tested and recorded. followed by another procedure to allow the automatic system to be reset & put back on, + expensive. Peter
mattyturton  
#4 Posted : 27 May 2011 12:08:28(UTC)
Rank: Forum user
mattyturton

Hi Bob

I am the H&S manager on the site, do not have any background in gas though and have today been asked the question.


Thanks Peter, I will have a look and see what I can find on the website.

bob youel  
#5 Posted : 27 May 2011 14:46:57(UTC)
Rank: Super forum user
bob youel

M
Thanks; I think that U know where I am coming from



Also speak to your local building regs and fire people for their thoughts as this is not a new question so they [the experts] may have a history to give U
chas  
#6 Posted : 27 May 2011 14:54:40(UTC)
Rank: Super forum user
chas

If you are referring to DT classrooms, BS4163 - COP for design of DT areas says the following;

Mains gas installations........

NOTE The Gas Act 1985, amended Gas Act 1995 and the Gas Safety
(Installation and Use) Regulations 1998 (as amended) apply to gas
installations. It is essential that all work on gas appliances is carried out
by an HSE approved installer.

5.3.1 Main isolator.....
Emergency control valves should be situated as follows:
• as near as practicable to the point where the gas supply enters the
building, either internally or externally;
• in a readily accessible position;
• so that the key or lever (handle) is parallel to the pipe when the
valve is open and pulled down to close;
• with a test point fitted downstream of each valve.
NOTE The emergency control valve key or lever should be securely
attached to the valve.
Emergency control valves should be clearly labelled.

Room isolation.......

Design and technology work areas with gas equipment should have a
means of isolating the gas supply to the room. The means of isolation
should be in a readily accessible position and should be clearly marked,
but should not be readily accessible to students. The means of isolation
should be either a manual valve, or a fail-safe electrically operated
solenoid valve that may form part of an emergency stop system within
the room.

Fixed installations using liquefied petroleum gas......

Liquefied petroleum gas (LPG) should be supplied by hard pipe from
cylinders located outside the building in the open air. Cylinders should
be securely fixed in an upright position with the valve uppermost.
Manifold systems should incorporate a main shut-off valve and a
regulator downstream (appropriately set), and a non-return valve
downstream of these.
NOTE It is essential that all work on these appliances is carried out by
an HSE approved installer.
LPG fired appliances should be fitted with appropriate safeguards
(e.g. flame failure devices, shut-off valves, pilot burners).

Science classrooms may differ. Hope this helps
Ron Hunter  
#7 Posted : 27 May 2011 15:04:52(UTC)
Rank: Super forum user
Ron Hunter

IGEM reissued IGEM/UP/11 'Gas installations for educational establishments' last June (2010) and there are perhaps some issues ofmisinterpretation out there.
My reading is that a manual shut-off is perfectly adequate in technical and food science rooms provided it is in a readily accessible position for use by teaching and technical staff.

Only where it is not practicable to install a manual isolation valve in a readily accessible position, or where it is required to interlock the gas supply with other safety systems such as air flow, fire or gas detection is an automatic means of isolation required.

You can read a precis of IGEM/UP/11 at the IGEM website. A bit pricey to buy though.
chas  
#8 Posted : 27 May 2011 16:39:19(UTC)
Rank: Super forum user
chas

Oops...I fell foul of the Mods and copyright issues, apologies. In short you can have either a manual or auto gas shut off. Refer to BS4163
Users browsing this topic
Guest
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.