Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
ianjones  
#1 Posted : 26 March 2012 15:53:43(UTC)
Rank: Forum user
ianjones

We have a engineer with electrical experience but no qualifications, who carries out minor electrical repairs, maintenance and installations to 240v and 3 phase equipment from existing electrical boxes.

I believe that in order to prove competence he should take the 17th edition regs.

MY engineer manager believes that his repairs are on 'protected systems' i.e. Fault finding on control systems where no live parts are accessible, he isolates when changing electrical parts etc and any installations are normally just running new cable from existing access points.

Any other work is done by electrical contractors.

what do you feel? I just feel I cannot prove competence in the event of an incident (either to him or though a mistake)
PIKEMAN  
#2 Posted : 26 March 2012 16:36:52(UTC)
Rank: Super forum user
PIKEMAN

I feel that you have answered this your self by stating "minor" repairs.

If this person is competent to do minor repairs then why would you need them to do the wiring regs course? Perhaps you could document their competence in some other way.

Of course, this depend on the definition of minor work......
Ron Hunter  
#3 Posted : 26 March 2012 16:37:43(UTC)
Rank: Super forum user
Ron Hunter

A cautionary tale: Engineers in such situations may be lucky to escape serious injury when they are totally unaware that modern emergency lighting units also have a separate maintained mains supply (for trickle charging) - they may think the whole circuit is isolated when it is not!
I suggest you don't wait until a similar accident. In the not-so-hypothetical scenario I describe, the engineer was lucky enough to escape serious injury........
Zimmy  
#4 Posted : 26 March 2012 19:22:57(UTC)
Rank: Super forum user
Zimmy

With the greatest respect to all concerned.

Any electrical work needs to be tested. If he cannot install to the 17th and test to C&G 2391 he has no reason to be doing the work. Who certifies the work? Not him I hope?

If the naughty stuff hits the rotor blades then

Please, please refer to the electricity at Work act 1989 before someone gets killed. And what he means by 'protected systems' is anyones guess.

Someone is going to get hurt here.
paul.skyrme  
#5 Posted : 26 March 2012 19:30:37(UTC)
Rank: Super forum user
paul.skyrme

ian,
Just curious what his degree is in if not electrical and he has electrical experience?
m  
#6 Posted : 26 March 2012 19:32:35(UTC)
Rank: Super forum user
m

From the OP's original description it looks to me as if the work is more akin to test engineering rather than electrical installation. Perhaps a more appropriate qualification is something like an ONC, then later, HNC in electrical & electronic engineering.
Grizzly  
#7 Posted : 26 March 2012 20:12:15(UTC)
Rank: Forum user
Grizzly

paul.skyrme wrote:
ian,
Just curious what his degree is in if not electrical and he has electrical experience?


I'm sure you know as well as anyone that, just because someone is described as an 'engineer', it doesn't mean that they have an engineering degree, or similar qualification.
ianjones  
#8 Posted : 26 March 2012 21:30:17(UTC)
Rank: Forum user
ianjones

Hi

a bit more info is required

these are production engineers, apprenticeship and years of experience
definitely not hnc or any form of qualification

the electrical work is generally if a machine goes down
the engineer tests it through basic fault finding and then replaces any part - no live working

any installation would be running a power lead from an existing power supply to a machine
nothing else

anything else is done by contractors

they are thousands of engineers of these competencies in factories across UK
so I am interested to see how others cope

we are not a large site so cant afford a dedicated electrical engineer and we would have to have 3
to ensure 24/7 cover.
boblewis  
#9 Posted : 26 March 2012 21:30:37(UTC)
Rank: Super forum user
boblewis

This is always a thorny issue and ultimately competence for a task is employer defined. If you think about it almost every electrical goods you buy have been constructed and tested by non 17th edition persons. There has to be a range of tasks where job training and/or other electrical training are actually more suitable than the 17th edition. In fact I would prefer that this is so as the 17th ed. does not cover much of what is required for manufacturing and instrumentation/testing.

Bob
Ron Hunter  
#10 Posted : 26 March 2012 22:51:36(UTC)
Rank: Super forum user
Ron Hunter

Perhaps Paul alludes to the fudge that followed the Finniston Report on the Engineering profession c.1980.
There was an opportunity back then to confirm the term "engineer" as conferring status on qualified professionals, in a similar fashion to that in Germany.
Sadly not to be and these days, anyone can call themselves "an engineer".
Kudos to you Paul, I was once proud to call myself a Mechanical Engineer.
bob youel  
#11 Posted : 27 March 2012 07:25:21(UTC)
Rank: Super forum user
bob youel

Whilst offering no disrespect here we are probably talking about some sort of 'grandfather' competence which may not hold up in a court these days and as Bob L has said the 17th edition is not really geared up for industrial working

My advice is to get some update electrical training as such training should be an on going activity in any case
paul.skyrme  
#12 Posted : 27 March 2012 22:28:34(UTC)
Rank: Super forum user
paul.skyrme


I think we need to get a few facts down here.
17th edition qualification. This is a few days in the classroom, then an open book, on line, multi-choice exam based solely on the current version of BS7671, that is Amd1 2011.
This is not an electrical engineering course.
It is not an electrical installations or maintenance course.
In fact it is not a practical course of any kind.
It is merely an exam on how to find your way around the 17th ed.
It just raises your awareness of what is in the wiring regulations and how to find it.
Next, BS7671 DOES cover industrial installations.
BS7671/17th covers the fixed wiring in buildings that is not the responsibility of the DNO up to the point of connection of current consuming equipment, whether that be via a plug, e.g. a 13A socket outlet to power your laptop, or a £1M machine tool which has a single point of connection to the fixed building wiring.
However, neither your laptop or the machine are covered by BS7671.
Both your laptop and the £1M machine tool are designed and built to different standards.
The "equivalent" to BS7671 for machinery is BS EN 60204-1 in its current guise.
Also you will have the Machinery and Low Voltage Directives and the other associated product standards to contend with.

There is no equivalent to the C&G 17th course for 60204 for a very good reason.
Please remember that BS7671/17th edition does not apply to machinery.
If the so called Engineer is working on the fixed wiring in the premises then his work really should comply to BS7671, if he is not qualified in the regs & I&T then it would be difficult to prove his competence.
If he is working on the fixed wiring does he have the correct calibrated test equipment to meet the requirements of BS7671?
Does he have the competence to complete the BS7671 certificates for his work?
If not he should not be doing the work.

If he is working on machinery then a whole new level of competence is required.
This is not taught by a single C&G course over 3 days.

ian,
I am concerned that you are allowing production engineers to work on electrical systems.
This would not be taught on any production engineering course I suspect.

There seems to be some misuse or misunderstanding of terms here.

I doubt that it would be possible to fault find on machinery without live working, this is one of the areas that HSE will allow live working, it is also a very dangerous situation.
Not necessarily just from the electrical risks, but, it can also be from the existing fault on the machine resulting in unexpected machine "behaviour"!
I am also curious why you need 3 electrical engineers.
All you actually need is 3 machinery maintenance electricians.
Why get professional engineers to fix machines?

I feel that your employer is out on a limb here as are thousands throughout the UK, it is just by luck that they survive!
It may be your business insurer that will be the one who will be your downfall in the event of an incident.
Check your small print!
Mind many of them don't understand the differences between the fixed electrical installations in the building and the electrical equipment of machinery.
There are also a lot of electricians who struggle too!
There is more to the electrical lark than meets the eye you know!
;)


Grizzly,
I am not even getting on to that soap box!
I have very strong opinions on this subject which will get me banned from the forum.
Just to say I HATE the misuse of the term engineer.
I'm sure that if everyone who had even had a days H&S training called themselves a H&S consultant then there would be a riot on here.
However, that is the only parallel I feel I can draw upon.
I am not going to discuss or elaborate on this area any more.
boblewis  
#13 Posted : 28 March 2012 00:16:13(UTC)
Rank: Super forum user
boblewis

Paul

Agree with much you say. Most electrical installers are generally time served via city and guilds or via the modern NVQ programmes and modern apprenticeships. A significant percentage are not graduates even when their title includes the infamous term engineer. The 17th edition for me is simply the code by by which installations are undertaken, tested and in general maintained. But it is a code and can be rejected by the employer should they feel their arrangements match those given.

I carefully distinguished manufacturing because this is a clear example where 17th edition has no place as also might occur in maintenance of boiler and other instrumentation, including connection to a system. But I think we can both agree that 17th is not the be all and end all of electrical competence - it is perhaps a part of the mix for some roles but not others.

Bob
ianjones  
#14 Posted : 28 March 2012 10:28:46(UTC)
Rank: Forum user
ianjones

Thank you guys

and here in lies the problem - I identified that 17th edition wasn't the best route for us
so what was? That was were I hit this issue that they is no obvious competence qualification for industrial machinery

I take on board al the issues about the status of an 'engineer' I use the term simply because that is the role used at this site to describe their contract HNC or other are not a requirement.

As always in our role, I am adviser to management and I give the best advice possible along with nudges, ideas, legislation and ACOP's guidance and what if scenario's

thank you very much for input all , which has been very useful.
smitch  
#15 Posted : 28 March 2012 10:53:58(UTC)
Rank: Forum user
smitch

Ian

you have pm
Zimmy  
#16 Posted : 29 March 2012 18:32:02(UTC)
Rank: Super forum user
Zimmy

Listen to P.S. He really does know wat he is about. I teach 17th and inspection and testing etc For me,I'd handcuff the bloke and get a real electrician on the job
Users browsing this topic
Guest (3)
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.