#1 Posted : 01 June 2017 13:57:42(UTC)
Rank: Super forum user
chris42

Workplaces, especially offices tend to be rearranged in layout on a relatively regular basis in all the places I have regularly worked. This inevitably means that the electrical sockets are in the wrong place / not enough of them or the new printer cable is 100mm shorter than the last one, therefore extension leads tend to get used. Now in offices the items used on an extension lead are mostly low powered ie monitors, printers, laptop docking station etc, but may not be. 

My question is, has anyone come up with a nice easy way to ensure that people don’t overload these extension leads?

Do you move everything about and someone does the calculation on the loading of that extension lead and no one touches it thereafter until the next move?

Or  

Do you have something marked on the plugs / cables of all equipment (or colour coded etc) so the user can just ensure they are not going to overload by doing a simple addition of what is already plugged in.

Or

something else.

Yes, getting an electrician in and the whole office rewired every time there is a new starter and the desks move is obviously the best, but not necessarily practical each and every time. Extension leads are not illegal, but cause FRA’s the jitters when they see them.

How do you control their use?

Chris

Bob Hansler  
#2 Posted : 01 June 2017 14:43:16(UTC)
Rank: Forum user
Bob Hansler

You have mail Chris and my number mate

Rob

Bob Hansler  
#3 Posted : 01 June 2017 14:48:57(UTC)
Rank: Forum user
Bob Hansler

http://www.electricalsafetyfirst.org.uk/guides-and-advice/electrical-items/overloading-sockets/

The above is OK  but not really right (but to go into it deep would bore the pants off yo uall)

Rob

chris42  
#4 Posted : 01 June 2017 15:47:22(UTC)
Rank: Super forum user
chris42

Thanks Bob, I noticed you seem to visit the site more regularly again.

Sorry perhaps not clear in my post, I'm ok with having to work out what is being used etc so not to overload, it’s just other people! 

Hence my question, do you get a "non-muppet" to work out and then they are not allowed to alter or has anyone come up with a novel solution.

I was wondering if say we put a tag near the plug telling them the current draw (amps) to save them having to work it out or manhandle bits of equipment to get to the info. Then all they need to know is not more than 13A in total (if it is a 13A extension) ie

Laptop                            0.5a             65W

Monitor                           0.5a           100W

Hoover                              9a          2000W

These three in a 13amp extension would be ok for instance, but if you added a kettle it would not be.

I just know that people will change things around between my visits, and was hoping someone had come up with a Muppet proof system. I don’t want to say sorry you are not competent to plug anything in, but I want to have something really easy so they don’t accidently overload an extension.

Yes, I know, stop employing muppets, but is there a test for that? and I’m not given a vote on new recruits anyway.

So how does everyone do it.

Chris

Bob Hansler  
#5 Posted : 02 June 2017 07:41:09(UTC)
Rank: Forum user
Bob Hansler

Hi Chris ( Not been banned for a while as until now no one seems to have noticed - time will tell) :-)

The fuse at the origin lead will be 13A at most (unless a hair clip etc. has been used) so the max current on the ten or so multi outlet leads will be a little above the 13A for a shot time then the fuse should open.

If the other leads are 'over loaded' it will be the first fuse that should open.

I would suggest that as lond as the leads are un-coiled then the initial fuse will cover the rest?

I'd be worried about tripping etc.   

However, if 13A is drawn from evey outlet on the ring circuit (32A) then the 32A should open.

The main problem is the square type multi outlet units that strain the internals of the socket outlet due to the weight of the leads forsing the contacts apart and this will cause over heating and fires due to the minimal contact area within the unit.

I hope this hepls some of yo u:-) 

paul.skyrme  
#6 Posted : 02 June 2017 07:55:11(UTC)
Rank: Super forum user
paul.skyrme

Rob has just beaten me to posting.

Strictly speaking the 13A fuse within the BS1363 plug should be adequate to protect the extension lead from overloading, as long as the lead is designed and manufactured in accordance with the relevant standards.

IF it is compliant then it should be able to take the 13A load indefinitely, and hopefully the potential small overload for long duration, and, the over current which will open the fuse.

The most difficult to prevent is the small overload of long duration, say 14 or 15A, or perhaps even up to 20A.

This is where as Rob says it gets boring, it's the time/current characteristics that get you! ;)

One thing you need to be very careful with is long extension leads, and, "daisy chaining" of leads.

Invictus  
#7 Posted : 02 June 2017 08:11:09(UTC)
Rank: Super forum user
Invictus

Chris, i use this link http://www.electricalsafetyfirst.org.uk/ it's only a guide but we also use it to make our fire wardens aware.

chris42  
#8 Posted : 02 June 2017 08:19:26(UTC)
Rank: Super forum user
chris42

Thanks both

Yes, we insist on fully uncoiling any coiled extension leads, and no daisy chaining allowed.

So, from what you are saying, is that if they accidentally go over the 13a total of the extension then the fuse would blow and return it to a safe condition, so I should not be so concerned. However, if the current is just over the 13A for a period of time then this may not be quite enough for the fuse to go, but there may be a heating effect on the extension at some point. 

I don’t actually think we have any instances where we are overloading, but want a more proportionate approach that I can detail, than that of our FRA who feels no one should ever use an extension lead, ever, ever, ever. Our office ones are mainly just normal low powered office equipment and things like the vacuum are plugged into a wall socket to be honest. Outside of the office extensions are used as we require to use the odd power tool etc away from a wall and can’t have overhead supplies. But it then is one extension with one thing plugged into it and fully uncoiled.

I thought if I had a written method of control and simple process it would remove the backside covering none proportionate notes of the FRA.

Also thanks Invictus, off to look at your link and a reference mad by Bob

Cheers

Chris

Bob Hansler  
#9 Posted : 02 June 2017 09:22:05(UTC)
Rank: Forum user
Bob Hansler

and Paul and I have not started on max Zs either, where under fault conditions the fault current may not open the fuse for some considerable length of time causing the cable to heat up (a lot).  Handy for drying clothes but not the best plan.  If you look up in-service inspeation and testing (PAT if you like) you will note that there is a max length of lead before an RCD should be used.  Also worth noting is the conductor size or the flex.  Under NO circumstanses try and wire a 2.5mm flex into a 13A plug top.

Happy days

chris42  
#10 Posted : 02 June 2017 10:30:16(UTC)
Rank: Super forum user
chris42

Thanks Bob - yes Max Zs sound fun, and its not how much sleep you can get - well it is Friday :o)

Looked up the issue about RCD and max lenght of cable, didn't know that so thanks, found this link that others may be interested in so thought I would share.

electrical.theiet.org/wiring-matters/21/site-safety.cfm?type=pdf

or if link does not work search "2006 21 winter wiring matters site safety portable electric tools"

Seems quite practical advice.

Cheers

Chris

Captcha = DuNZs1Y  or could be read "Dunce i  Yes"

Stuart Smiles  
#11 Posted : 02 June 2017 10:58:01(UTC)
Rank: Forum user
Stuart Smiles

focus on kettles, hoovers, transformer 110v power tools, and have a place for them where they plug directly into a wall socket from own lead, so then you are only dealing/reviewing "lower power items" on the extension leads? 

big printers as well direct to lead and any ups/server so it can be "not unplugged in error", hopefully then you have a lesser problem to address - smaller items which are more mobile. 

also look at transformers, as a number of pat tests on some when have been squashed/covers damaged? 

perhaps an area for mobile chargers in canteen with usb charge sockets for mobiles to restrict everyone has chargers brought in for iphones/androids, poss same for meeting rooms - heat used by projectors is massive so plug in to mains outlet or specific wiring, mobile charging if people are in there for "a day".

would it be worth changing plug covers for round ones for cleaner/hoover socket? 

 

Ron Hunter  
#12 Posted : 02 June 2017 12:38:17(UTC)
Rank: Super forum user
Ron Hunter

Use of extensions increases risk of cumulative leakage currents exceeding safe limits under fault conditions.

Longer power cables are usually readily available, and position of printers etc. is often limited by the practical length of USB cabling.

Our house rule is extensions are for temporary use only (and no daisy chaining!)

paul.skyrme  
#13 Posted : 02 June 2017 15:49:37(UTC)
Rank: Super forum user
paul.skyrme

Originally Posted by: Ron Hunter Go to Quoted Post

Use of extensions increases risk of cumulative leakage currents exceeding safe limits under fault conditions.

Longer power cables are usually readily available, and position of printers etc. is often limited by the practical length of USB cabling.

Our house rule is extensions are for temporary use only (and no daisy chaining!)

Ron,

That's not quite exactly the issue, yes there will be a minute increase in potential leakage proportional to the insulation resistance of the cable, plugs etc.

The main issue is the increase in earth fault loop impedance to ensure automatic disconnection of supply (ADS) in the event of a fault.

As an aside, there is a "fight" here between product standards which require ever shorter supply flexes so that things cannot be used a great distance from sockets, manufacturers of appliances profiteering from using shorter supply flexes whilst charging the same for the product as they used to do with a longer flex, and, the product standards that allow cables to be smaller than for example would be allowed for the power rating requirements under BS7671 because they are less than a certain length.  The exact detail varies.

However, this then leaves the end users in an enterprise left holding the baby as it were, leads are too short to be of any use, and extension leads are shunned, there are inadequate sockets suitably located, etc.

Extension leads are perfetly safe, as long as they are used within the guidance issued by for example the Electricity Safety Council, and the IET, and HSE.

I do some Pro Bono work for a local Chapel, including electrical repairs as I am still covered for this, and the members were forever bringing in dodgy leads, so I skipped the lot & made two one gang extensions from blue "arctic" flex.  The only other things I will allow to remain there are multiway adaptors in good condition, or roll up leads in good condition.  All of the members of my family that use the Chapel are nore than aware that extension leads need to be unwound before use, and they know I will check if I am there when they are in use.

With one of the "arctic" flex extensions, the whole of the downstairs of the building can be covered with it connected to the nearest socket to where you are doing whatever you are doing.

If I see anything I don't like I simply remove it and store it, and await the complaint, there hasn't been one yet! ;)

I inspect stuff regularly whenever I go there, and PAT them as I see fit.

Stuart Smiles  
#14 Posted : 02 June 2017 18:10:57(UTC)
Rank: Forum user
Stuart Smiles

have a look at

cpc, rswww.com and netshop.co.uk

you can get longer kettle leads, appropriate to your length needs,

or adapters for kettle to kettle connections (usually used in switch rooms/comms cabinets to allow you to remove international plug type adaption requirements. 

don't know if you want to look at class b,c,d, circuit breakers, or if it's appropriate in your setup for slower trip, or if you need to move the otherway, or could install a new ring for computers and split load? 

can you shorten the circuits to make them less likely to take too long to trip,

or use thicker wiring for specific circuits or new additional spurs and remove sockets further away / extensions on the end of them

could you put in a db closer to the ring main/circuit so that there is less distance to travel like that, on the end of a new spur? 

had lots of problems like this, but the electrician's answer seems to usually be re-wire and renew... new db boards etc 

have you got a wiring diagram and/or is it all labelled/ can it be surveyed before going to next steps and options plan.

paul.skyrme  
#15 Posted : 02 June 2017 19:33:48(UTC)
Rank: Super forum user
paul.skyrme

Stuart,

Please be careful of what you recommend, trip times are defined in BS7671 and must be met, the changing of breaker characteristics must only be done with serious consideration.

The existing breakers are probably b or c curve, possibly, as you move from b to c to d the required earth fault loop impedance drops, thus, this makes the use of extension leads more difficult to allow.

There is a reason appliance leads are short.  One also must be aware that many "kettle leads" are not rated for a 3kW load.

"Daisy chaining" IEC leads is bad practice electrically, especially for permenant use.

The reason that Rob & I have been mentioning trip times is because as the EFLI increases as does the trip time.

Circuit breakers have a finite minimum trip time, taken generally as 0.1s, thus no matter how short you make the circuit it won't trip in <0.1s as the MCB is a mechanical device which has a finite reaction time.

"Thicker wiring" will reduce the EFLI, but, if it is already compliant with the requirements for ADS under BS7671 why change?

Curious as to why you are suggesting a spur, that should be only used as a get out of jail card really.

Stuart Smiles  
#16 Posted : 03 June 2017 12:25:01(UTC)
Rank: Forum user
Stuart Smiles

Paul,

Suggested that the use of various breakers as they may solve some tripping issues where appropriate, (note caveat placed on where appropriate). 

suggested additional ring if that would assist splitting load and (at the same time) perhaps could provide benefit by moving sockets off existing to a new supply.

we relatively recently had a seperate supply installed for a computer room, (was using ring main), however sometimes had had the circuit trip.

what we decided to do was to put a spur to a local db (for that room) and sockets off it to enable localised isolation and at the same time, additional "Commando" sockets for 2x upses, to then distribute the power within the cabinet we used pdu's with kettle lead connections - note mention of kettle-kettle leads of various lengths 

with some of the cables for server/other devices, we needed approx 3m rather than 0.75 to 1m leads (as has been mentioned ref leads getting shorter, so we bought a selection of different length leads to cable appropriately within the cabinet. (also re-used in some locations for longer leads required in office as had them to hand. - bought both moulded with uk plug and kettle(m)-kettle(f).

as such, I mentioned that such leads are available, and as such could solve the problem with a longer lead from computer to wall (as well as short computer lead & extension) - direct connection to socket rather than on an x-gang extension lead. 

In addition, transformers/mobile chargers seem to be everywhere these days, and it will always be a challenge to pat test when brought in by users, so perhaps use of sockets with usb, (with strategic locations that people will use), could provide a way of removing the desire to use such devices. We typically found at pat testing some devices had been damaged plastic or lead pulled and required some replacements when found. 

with reference to tripping of devices a long way from the rcd, some devices we had to use slower trip circuit breakers,(welder &extension on specific socket) - had multiple discussions ref where additional sockets could be, and installed some, but it always had to be next to work-piece and "mobile" - hence extension. - this caused an issue with nusiance tripping so looked at moving down breakers, where it plugged in specifically, moved sockets nearer to db, shortened lengths of extension.  

With other circuits, normally we were going the other way, especially with the new db installation,(b) (and in addition, the new sockets meant that the area covered was significantly diminished, so distance from "last point" to rcd was a lot shorter, and load on the former ring was removed, so it became less of an issue with other devices. 

tripping was on a morning, and eventually found people were using electric fan heaters "cos it's cold", so we changed heating times on the boiler, and i migrated a couple of the heaters to a locked room, and gave them fleeces to wear, seemed to be the actual problem solved. for the ring main, main computers weren't tripping any more so less of an impact on others than was.  

again, the benefit of the seperate supply meant that it was in a secure computer room, unlikely to be affected by other devices overloading the ring or having too much on the circuit at the same time, no hoovering. 

at the same time, as a dr measure, we installed a switch-over so we could provide a proportion of power the site via a plug in generator - un-affecting dbs at the time of an outage.

this was because we had had a damaged main cable in the past, and a generator would provide an option to get doors up, and provide some basic functionality without having to take generator to location and apply power from a generator locally to open a roller shutter door in a power cut. - doing a manual paper system and then re-entering data is not fun.  

we always had on-going discussions ref fixed and pat electrics, and I ended up doing the wiring regs c&g course to understand more of the problem so that could evaluate different options with the electricians.

I would advocate same to others, so that can communicate in same language, reference docs, and design together what is an appropriate solution for your environment, taking account of people, activities and sensitivity to maintenance, outage, recovery etc. 

paul.skyrme  
#17 Posted : 03 June 2017 12:46:38(UTC)
Rank: Super forum user
paul.skyrme

Stuart,

I believe that you are mixing up a spur, which is concept unique to a ring final circuit, and a sub-main to a distribution board.

Please realise the limitations of the wiring regulations course, it is designed for competent electricians to find their way around the document, it is certainly not an electrical design course by a long shot, the current electrical design course is the C&G 2396 or EAL equivalent.

Edited by user 03 June 2017 12:48:19(UTC)  | Reason: Clicked wrong button!

Stuart Smiles  
#18 Posted : 03 June 2017 13:21:42(UTC)
Rank: Forum user
Stuart Smiles

I had responsibility for iso management systems of the site, electrics, and paying the bills. 

I wanted to know what I was paying for, why, and what the options were. 

Over a large site, with lots of requirements, someone has to discuss with contractors about oversight of everything, and that person was me. 

In addition, I would state that I have seen some people "retain" information from operators so that the "right decision" is made, it is beneficial to evaluate who it is "right" for, and to evaluate what's behind the decision making process, because sometimes underlying assumptions/decisions aren't always in line with everyone's view.  

Good documentation is always worthwhile, and as such knowledge of the system's setup can be invaluable, and I feel an activist approach towards the electrical requirements of the business helps to understand what you are being asked to pay for, why it's important, and provide less of a shock when invoices come in, and lists of outstanding work are being reviewed, and clearing off work completed from a test report.

In addition, as most will understand, budgets are always limited, and investment needs to be targeted appropriately, sometimes I would feel that there was a desire to remove/replace equipment when that may have had a different option as a method of addressing the problem.

some replacements, are definitely worthwhile - emergency lights to LED for example, (remedial decoration not included) however serious thought needs to go into other activities before planning to do "a list" over a weekend. 

in addition from a dr perspective, it is always good to know where the important switches are (and those to not turn off), so that the person assisting with activities on site knows where things are to support whatever activities are required.

I would advocate to anyone taking responsibility for a site that they should understand more about the "electrics" what's it do, why are they where they are, what do we have/need etc. 

Bob Hansler  
#19 Posted : 04 June 2017 11:00:30(UTC)
Rank: Forum user
Bob Hansler

Dear readers

I can assure you all that Paul and I are more than qualified to to design, erect and verify electrical installations.  

Kind regards

UncleFester  
#20 Posted : 05 June 2017 07:01:30(UTC)
Rank: Forum user
UncleFester

Originally Posted by: chris42 Go to Quoted Post

My question is, has anyone come up with a nice easy way to ensure that people don’t overload these extension leads?

How do you control their use?

Chris

In the past I've calculated the current taken by the item and written this numerically on the plug top - i.e. 1000W rated appliance / 230v = 5 rounded up. I've then instructed all staff and maintained toolbox talks that when using extension cables, the maximum that all plug labels in the extension sockets should not exceed a total of 13, being the fuse rating of the plug in the extension lead.

Guys doing the PAT whould ensure that the number rating on the plug top was clear and legible.

Simple to understand and audit.

Invictus  
#21 Posted : 05 June 2017 07:07:01(UTC)
Rank: Super forum user
Invictus

As stated we as part of fire warden training we include the use of extension leads particularly overloading them. We have the information on the plug top and a notice on the extension itself about what capacity it can take. We also try to group items together so in an office we might use an extension lead for the computer etc. we do not allow kettles etc in offices.

chris42  
#22 Posted : 05 June 2017 09:11:10(UTC)
Rank: Super forum user
chris42

Originally Posted by: UncleFester Go to Quoted Post
Originally Posted by: chris42 Go to Quoted Post

My question is, has anyone come up with a nice easy way to ensure that people don’t overload these extension leads?

How do you control their use?

Chris

In the past I've calculated the current taken by the item and written this numerically on the plug top - i.e. 1000W rated appliance / 230v = 5 rounded up. I've then instructed all staff and maintained toolbox talks that when using extension cables, the maximum that all plug labels in the extension sockets should not exceed a total of 13, being the fuse rating of the plug in the extension lead.

Guys doing the PAT whould ensure that the number rating on the plug top was clear and legible.

Simple to understand and audit.

Yes, that is what I was thinking unfortunately our PAT test person puts his sticker on the plug, So I was considering a little tag with the number on it attached to the wire near the plug (possibly colour coded to see at a glance).

Interesting idea about grouping Invictus, yes, we would not allow kettles in an office, but you would be surprised where they can be hidden. In a previous life, I once found a microwave, kettle and toaster in a metal filing cabinet on the workshop floor. Also, it is the other items such as little fan heaters that pop up from time to time (hate them) and who knows what else the little darlings may get their hands on. 

Cheers all

Chris