Paul,
Suggested that the use of various breakers as they may solve some tripping issues where appropriate, (note caveat placed on where appropriate).
suggested additional ring if that would assist splitting load and (at the same time) perhaps could provide benefit by moving sockets off existing to a new supply.
we relatively recently had a seperate supply installed for a computer room, (was using ring main), however sometimes had had the circuit trip.
what we decided to do was to put a spur to a local db (for that room) and sockets off it to enable localised isolation and at the same time, additional "Commando" sockets for 2x upses,
to then distribute the power within the cabinet we used pdu's with kettle lead connections - note mention of kettle-kettle leads of various lengths
with some of the cables for server/other devices, we needed approx 3m rather than 0.75 to 1m leads (as has been mentioned ref leads getting shorter, so we bought a selection of different length leads to cable appropriately within the cabinet. (also re-used in some locations for longer leads required in office as had them to hand. - bought both moulded with uk plug and kettle(m)-kettle(f).
as such, I mentioned that such leads are available, and as such could solve the problem with a longer lead from computer to wall (as well as short computer lead & extension) - direct connection to socket rather than on an x-gang extension lead.
In addition, transformers/mobile chargers seem to be everywhere these days, and it will always be a challenge to pat test when brought in by users, so perhaps use of sockets with usb, (with strategic locations that people will use), could provide a way of removing the desire to use such devices. We typically found at pat testing some devices had been damaged plastic or lead pulled and required some replacements when found.
with reference to tripping of devices a long way from the rcd, some devices we had to use slower trip circuit breakers,(welder &extension on specific socket) - had multiple discussions ref where additional sockets could be, and installed some, but it always had to be next to work-piece and "mobile" - hence extension. - this caused an issue with nusiance tripping so looked at moving down breakers, where it plugged in specifically, moved sockets nearer to db, shortened lengths of extension.
With other circuits, normally we were going the other way, especially with the new db installation,(b) (and in addition, the new sockets meant that the area covered was significantly diminished, so distance from "last point" to rcd was a lot shorter, and load on the former ring was removed, so it became less of an issue with other devices.
tripping was on a morning, and eventually found people were using electric fan heaters "cos it's cold", so we changed heating times on the boiler, and i migrated a couple of the heaters to a locked room, and gave them fleeces to wear, seemed to be the actual problem solved. for the ring main, main computers weren't tripping any more so less of an impact on others than was.
again, the benefit of the seperate supply meant that it was in a secure computer room, unlikely to be affected by other devices overloading the ring or having too much on the circuit at the same time, no hoovering.
at the same time, as a dr measure, we installed a switch-over so we could provide a proportion of power the site via a plug in generator - un-affecting dbs at the time of an outage.
this was because we had had a damaged main cable in the past, and a generator would provide an option to get doors up, and provide some basic functionality without having to take generator to location and apply power from a generator locally to open a roller shutter door in a power cut. - doing a manual paper system and then re-entering data is not fun.
we always had on-going discussions ref fixed and pat electrics, and I ended up doing the wiring regs c&g course to understand more of the problem so that could evaluate different options with the electricians.
I would advocate same to others, so that can communicate in same language, reference docs, and design together what is an appropriate solution for your environment, taking account of people, activities and sensitivity to maintenance, outage, recovery etc.