Rank: Guest
|
Posted By Ron Hunter Anyone help with a specific BS/EN reference stipulating as mandatory the provision of interlock devices to prevent the opening more than one drawer at a time? This is a 'fit for purpose' issue. Thankyou in anticipation.
|
|
|
|
Rank: Guest
|
Posted By Martin Cope Ron I have looked at the BSI web site and have extracted the following. If your issue is with safety the it may be worth looking at the Work place Regs.
BS 4438:1969 Specification for filing cabinets and suspended filing pockets 7 Safety requirements 7.1 The cabinet shall conform to BS EN 14073-2:20042). In addition, the cabinet shall conform to the requirements specified in 7.2 and 7.3. 7.2 Each card holder shall be fitted with a card on which shall be printed in red the word WARNING and notification that the cabinet is likely to topple if: 1) the upper drawer or drawers are loaded and pulled out when the lower drawer or drawers are empty; 2) a second drawer is pulled out before the first drawer is pushed back. 7.3 In order to prevent a cabinet from toppling when the drawers are disproportionately loaded, three holes of 7 mm (0.276 in) diameter shall be provided (one in the back and one in each side) so that the cabinet may be bolted to the wall or to the adjacent cabinet or cabinets. Alternatively, elongated holes of 7 mm (0.276 in) width may be provided to cater for vertical misalignment.
BS EN 14074:2004 Office furniture — Tables and desks and storage furniture —Test methods for the determination of strength and durability of moving parts 6.2.4 Interlock test When interlocks are fitted, one extension element shall be fully extended and an outward force of 200 N shall be applied to the handles of each of the remaining extension elements one at a time. The test shall be carried out a total of 10 times on each element. Record if the extension elements are retained closed.
5.5.1 Stability of the unloaded unit Place the unit on the floor surface (4.1). Open all doors to 90°. With the exception of any extension whose bottom front edge is =?300 mm above the floor, fully extend as many extension elements as possible without overriding the interlocks (if fitted). Open flaps to their horizontal position or as near horizontal as possible. Apply a vertical downwards load of 50N to any point likely to cause overturning, on the centreline of the front of an extension element and at 50 mm from the outer edge of a door or flap. Record whether the unit overturns.
BS EN 14073-3:2004 Office furniture —Storage furniture — Part 3: Test methods for the determination of stability and strength of the structure
5.5.2 Stability of the loaded unit Place the unit on the floor surface (4.1). Unless otherwise specified by the manufacturer, load all storage components with the load specified in Table 1.
Open all doors to 90°. With the exception of any extension element whose lower front edge is =300 mm above the floor, fully extend as many extension elements as possible without overriding the interlocks if fitted. Open flaps to their horizontal position or as near horizontal as possible.
Apply a vertical downwards force of 50 N to any point likely to cause overturning, on the centreline of the front of an extension element and at 50 mm from the outer edge of a door or flap. Record whether the unit overturns.
Hope this is of some use